Some of the larger freezers I had done, that were insured by a larger(est)
insurance company, were called out to use 165 temp in them, and not the 286
we normally apply to storage.

R/

MAtt

Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
 

----- >-----Original Message-----
----- >From: [EMAIL PROTECTED] 
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of [EMAIL PROTECTED]
----- >Sent: Wednesday, May 14, 2008 10:00 AM
----- >To: [email protected]
----- >Subject: Re: Sprinkler heads in coolers/freezers
----- >
----- >Ladies/Gentlemen:
----- >
----- >I can recall the early to mid-60's my father talking 
----- >about sprinklers in freezers/coolers - he was on the 
----- >daywork desk at Grinnell OF THE PACIFIC (Los Angeles). 
----- >Sprinklers activating in these 'boxes' were not an 
----- >uncommon "emergency" 
----- >call. Someone came up with the idea to put 212 F. 
----- >sprinklers in the freezers/coolers - and the emergency 
----- >calls eventually tapered off. I know of no reference in 
----- >NFPA-13 that addresses the temperature ratings of 
----- >sprinklers in walk-in feezers/coolers.
----- >
----- >People/Clients still ask me 'why in the world' would you 
----- >put sprinklers in walk-in coolers/freezers (or, for that 
----- >matter, swimming pool areas) - my response is an 
----- >inspection I did in a hotel restaurant several years ago 
----- >that was no longer in business. Inside the (rather 
----- >large) coolers and freezers, I found several rolls of 
----- >(rolled up) carpets. And, yes, there were sprinklers in 
----- >the boxes. When not in service, these areas make great 
----- >storage rooms!
----- >
----- >I believe the sprinkler activation issue in 
----- >freezers/coolers is that the cooling equipment can 
----- >malfunction and overheat - with no fire in the box - but 
----- >the temperature can rise in these insulated "rooms" and 
----- >trigger the 165 F. 
----- >sprinklers. I have designed, and specified, 200 F. 
----- >(Q.R.) sprinklers for these applications for a number of years.
----- >
----- >Regards to all...
----- >
----- >Jerry D. Watts, SFPE*
----- >ACCENT FIRE ENGINEERING INT'L. Ltd.
----- >Santa Fe/Albuquerque  San Diego, CA  Seattle, WA  Phoenix, AZ
----- >e: [EMAIL PROTECTED]
----- >(800) 503.1961
----- >web: www.accentfire.com
----- >
----- >*Society of Fire Protection Engineers and Rio Grande 
----- >Chapter (NM) Chapter/SFPE
----- >
----- >
----- >
----- >**************
----- >Wondering what's for Dinner Tonight? Get new twists on family 
----- >favorites at AOL Food.
----- >      
----- >(http://food.aol.com/dinner-tonight?NCID=aolfod00030000000001)
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to