I don't think you have to wait until the coolers are converted to
"miscellaneous storage boxes" - I would argue there are many materials
NORMALLY stored in these coolers and freezers that warrant sprinkler
protection: butter is one example.  But the other less combustible
material found in a cooler can burn, too.  And when the fire starts on
the inside, it could quickly spread to the cooler's insulating material,
resulting in a severe fire challenge.

Mark A. Sornsin, PE 
Fire Protection Engineer 
Ulteig Engineers, Inc. 
Fargo, ND  
701.280.8591
[EMAIL PROTECTED] 
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, May 14, 2008 10:00 AM
To: [email protected]
Subject: Re: Sprinkler heads in coolers/freezers

Ladies/Gentlemen:

I can recall the early to mid-60's my father talking about sprinklers in

freezers/coolers - he was on the daywork desk at Grinnell OF THE PACIFIC
(Los 
Angeles). Sprinklers activating in these 'boxes' were not an uncommon
"emergency" 
call. Someone came up with the idea to put 212 F. sprinklers in the 
freezers/coolers - and the emergency calls eventually tapered off. I
know of no 
reference in NFPA-13 that addresses the temperature ratings of
sprinklers in walk-in 
feezers/coolers.

People/Clients still ask me 'why in the world' would you put sprinklers
in 
walk-in coolers/freezers (or, for that matter, swimming pool areas) - my

response is an inspection I did in a hotel restaurant several years ago
that was no 
longer in business. Inside the (rather large) coolers and freezers, I
found 
several rolls of (rolled up) carpets. And, yes, there were sprinklers in
the 
boxes. When not in service, these areas make great storage rooms!

I believe the sprinkler activation issue in freezers/coolers is that the

cooling equipment can malfunction and overheat - with no fire in the box
- but the 
temperature can rise in these insulated "rooms" and trigger the 165 F. 
sprinklers. I have designed, and specified, 200 F. (Q.R.) sprinklers for
these 
applications for a number of years.

Regards to all...

Jerry D. Watts, SFPE*
ACCENT FIRE ENGINEERING INT'L. Ltd.
Santa Fe/Albuquerque  San Diego, CA  Seattle, WA  Phoenix, AZ
e: [EMAIL PROTECTED]
(800) 503.1961
web: www.accentfire.com

*Society of Fire Protection Engineers and Rio Grande Chapter (NM) 
Chapter/SFPE



**************
Wondering what's for Dinner Tonight? Get new twists on family 
favorites at AOL Food.
      
(http://food.aol.com/dinner-tonight?NCID=aolfod00030000000001)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to