I think NFPA 20 says no the the reducing valve.  Therefore, I believe it has
to go after the discharge pump control valve.   As stated, once you get past
that control valve, NFPA 20 is no longer governing the piping.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Wednesday, July 09, 2008 9:07 AM
To: [email protected]
Subject: Pressure reducing valve location for a fire pump

    I have to install a pressure reducing valve on the discharge side of the
fire pump.  I know from past discussions that if standpipes are present, the
valve must be installed after the last control valve for the fire pump to
satisfy NFPA 14.  What if this is a large warehouse falling strictly under
13?  Could it be placed between the pump discharge and check valve (just
like pressure relief valve on a diesel
FP) and sized per minimum relief valve in 2-20 (NFPA 20 99ed)?  I have a
2000gpm pump with a 8" discharge flange and would like to get a 8"
pressure reducing valve to work instead of a 10in (size required for
discharge pipe) to save some money.  I checked the spec sheets and the 8"
valve can handle the flow at 150%.
    
Thanks,
Dewayne
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

__________ NOD32 3255 (20080709) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to