D-man: Craig asked a couple of REALLY pertinent questions - what are the conditions of the application and what are you trying to accomplish?
Steve Leyton Protection Design & Consulting -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Dewayne Martinez Sent: Wednesday, July 09, 2008 9:40 AM To: [email protected] Subject: RE: Pressure reducing valve location for a fire pump Travis, Any idea where this is? I couldn't find it in the 99ed or the 07 ed. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack, SET Sent: Wednesday, July 09, 2008 11:29 AM To: [email protected] Subject: RE: Pressure reducing valve location for a fire pump I think NFPA 20 says no the the reducing valve. Therefore, I believe it has to go after the discharge pump control valve. As stated, once you get past that control valve, NFPA 20 is no longer governing the piping. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Dewayne Martinez Sent: Wednesday, July 09, 2008 9:07 AM To: [email protected] Subject: Pressure reducing valve location for a fire pump I have to install a pressure reducing valve on the discharge side of the fire pump. I know from past discussions that if standpipes are present, the valve must be installed after the last control valve for the fire pump to satisfy NFPA 14. What if this is a large warehouse falling strictly under 13? Could it be placed between the pump discharge and check valve (just like pressure relief valve on a diesel FP) and sized per minimum relief valve in 2-20 (NFPA 20 99ed)? I have a 2000gpm pump with a 8" discharge flange and would like to get a 8" pressure reducing valve to work instead of a 10in (size required for discharge pipe) to save some money. I checked the spec sheets and the 8" valve can handle the flow at 150%. Thanks, Dewayne _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) __________ NOD32 3255 (20080709) Information __________ This message was checked by NOD32 antivirus system. http://www.eset.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 3255 (20080709) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)
