OK, I'm a bit confused so help me out.

You have a potential project that will require high pressures which are
yet undefined,  so you are installing a pump with a total discharge
pressure of ????.

Is the purpose of the pressure reducing valve to protect other standard
175psi rated systems from the over pressure?




Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Wednesday, July 09, 2008 12:36 PM
To: [email protected]
Subject: RE: Pressure reducing valve location for a fire pump

I have been told that there will be a future freezer building that will
have a Quell system which requires the high pressures.  This is a new
installation.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, July 09, 2008 11:28 AM
To: [email protected]
Subject: RE: Pressure reducing valve location for a fire pump

What's the purpose of the reducing valve in this application?

Is this a new pump, existing pump, what are the design considerations
warranting this? 


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Wednesday, July 09, 2008 12:07 PM
To: [email protected]
Subject: Pressure reducing valve location for a fire pump

    I have to install a pressure reducing valve on the discharge side of
the fire pump.  I know from past discussions that if standpipes are
present, the valve must be installed after the last control valve for
the fire pump to satisfy NFPA 14.  What if this is a large warehouse
falling strictly under 13?  Could it be placed between the pump
discharge and check valve (just like pressure relief valve on a diesel
FP) and sized per minimum relief valve in 2-20 (NFPA 20 99ed)?  I have a
2000gpm pump with a 8" discharge flange and would like to get a 8"
pressure reducing valve to work instead of a 10in (size required for
discharge pipe) to save some money.  I checked the spec sheets and the
8" valve can handle the flow at 150%.
    
Thanks,
Dewayne
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to