That's far more gov't work than I can stomach each year. The other post,
tho, makes a lot of sense- let NAVFAC specify the pipe type!

Its so much easier to get an extra when the evidence you are pointing to,
when showing the problem, doesn't have your own logo atop it.

Like the C5A hanger that has a draft curtain down the middle of the center
system of 3 inat the roof, ensuring at least two of the 3 will dump. Like
the engineer that didn't realize churn was higher than rated pressure....
almost 20 years ago they ignored our contractor suggestions and we installed
what they specified, then after the acceptance test we removed the 250 GPM
foam pumps and installed 300's, plus swapping out the tanks for larger
ones....a lot of tax dollars went to Broadview Heights, OH that year.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Thursday, July 24, 2008 11:54 AM
To: [email protected]
Subject: Re: Deperming Pier

George,

Let Rick get that tax money. You're going to pay it out anyways and at
least it'll stay not only in America but in the industry. If he uses
cheap stuff the savings might go to a study by Canadian researchers on
the effects of Russian vodka on Egyptian dung beetles. I always try to
get enough government money each year to pay me back for last year's
taxes.

On Thu, Jul 24, 2008 at 6:27 AM, George Church <[EMAIL PROTECTED]> wrote:
> I'd be concerned about two things with CPVC-
> Effects of sunlight, even under the pier you'd likely get strong
reflections
> off the water; and where are you getting 6" CPVC?
> I have no idea if regular plumber's PVC would work; if you have a
> low-pressure DPV, and you're looking at a 2.5" DPV as your activating
device
> (and combo exhauster, it's a pretty big orifice) then wouldn't the air
never
> be at high pressure and so it shouldn't be a problem to use PVC?
>
> NFI, just a thought that would save my tax dollars versus SS316.
>
> glc
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of
> [EMAIL PROTECTED]
> Sent: Thursday, July 24, 2008 8:49 AM
> To: [email protected]
> Subject: RE: Deperming Pier
>
> What if you ran plastic, CPVC is approved for fire protection above grade
> per NFPA 13.  See 6.3 of NFPA 13, 2007.
>
>
>
>
>
>
> Craig L. Prahl, CET
> Fire Protection Group
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [EMAIL PROTECTED]
> http://www.ch2m.com
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Rick Green
> Sent: Thursday, July 24, 2008 8:19 AM
> To: [email protected]
> Subject: Deperming Pier
>
>
> I am installing a dry pipe system (no sprinklers) supplying four hose
valves
> on a pier.
>
> The dry pipe valve assembly is located in a heated area.  Extending out
from
> the dry pipe valve assembly  is 6" galvanized steel pipe.  The steel pipe
is
> routed below the pier out to the  location of four hose valves.
>
> The pier is used for Deperming ships, submarines.
>
> Deperming is a procedure for erasing the permanent magnetism from ships
and
> submarines<http://en.wikipedia.org/wiki/Submarines> to
> camouflage<http://en.wikipedia.org/wiki/Camouflage> them against magnetic
> detection vessels and enemy marine
> mines<http://en.wikipedia.org/wiki/Naval_mines>.
>
> Anyway, there is about a 200' section of the pier that requires that all
> materials be non-magnetic.
>
> *        Galvanized steel pipe that NAVY specified obviously want work.
>
> *        CPVC plastic pipe will not work because installing dry system -
> correct on this right?
>
> *        Provided them pricing for stainless steel, copper, brass and now
> they want pricing for Aluminum,.
>
> So a few questions
>
> o   Ever used aluminum pipe for sprinkler installations?
>
> o   Is there some other pipe type that I am not thinking about
>
> Help would be most appreciated.
>
> Rick E. Green
> District Manager
> East Coast Fire Protection, Inc.
> 1113 Cavalier Boulevard
> Chesapeake, Virginia 23323
> 757/485-7486(p), 757/295-0956(direct), 757/328-0131(cell) [EMAIL PROTECTED]
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to