You some type of fixture similar to a fire pump test header downstream
of the backflow preventer that is of a size sufficient to flow the
design demand. For a DOE project you may also be required to provide a
means of containing and capturing the water for subsequent treatment.
Forward flow testing is a requirement of NFPA 25.

On Mon, Aug 18, 2008 at 12:20 PM, Karen Purvis
<[EMAIL PROTECTED]> wrote:
> This is for a DOE project and the comment I received form them states; show
> the pipe and valve configuration at the sprinkler system riser that will be
> installed to perform the required forward flow test of the system backflow
> preventer. The pipe configuration and discharge point must be capable of
> flowing the design water demand for the system.
>
> I showed a detail that included a zurn backflow going to an alarm check and
> on up to the FDC then to the riser.
>