We've done a number of DOD projects and have used a Croker 6800 series Fire Pump Test Connection, between the FDC and The System. We then ordered a custom plate Branded just "Test Connection".
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Karen Purvis Sent: Monday, August 18, 2008 1:21 PM To: [email protected] Subject: RE: foward flow test This is for a DOE project and the comment I received form them states; show the pipe and valve configuration at the sprinkler system riser that will be installed to perform the required forward flow test of the system backflow preventer. The pipe configuration and discharge point must be capable of flowing the design water demand for the system. I showed a detail that included a zurn backflow going to an alarm check and on up to the FDC then to the riser. Karen Purvis Designer Facility Systems Consultants 714 S Gay St Knoxville, TN 37902 ph.865-246-0164 fax 865-246-1084 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG - http://www.avg.com Version: 8.0.138 / Virus Database: 270.6.5/1620 - Release Date: 8/19/2008 6:04 AM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)