> You some type of fixture similar to a fire pump test header downstream
> of the backflow preventer that is of a size sufficient to flow the
> design demand. For a DOE project you may also be required to provide a
> means of containing and capturing the water for subsequent treatment.
> Forward flow testing is a requirement of NFPA 25.
>
> On Mon, Aug 18, 2008 at 12:20 PM, Karen Purvis
> <[EMAIL PROTECTED]> wrote:
>> This is for a DOE project and the comment I received form them states; show
>> the pipe and valve configuration at the sprinkler system riser that will be
>> installed to perform the required forward flow test of the system backflow
>> preventer. The pipe configuration and discharge point must be capable of
>> flowing the design water demand for the system.
>>
>> I showed a detail that included a zurn backflow going to an alarm check and
>> on up to the FDC then to the riser.
>>
>> Karen Purvis
>> Designer
>> Facility Systems Consultants
>> 714 S Gay St
>> Knoxville, TN 37902
>> ph.865-246-0164
>> fax 865-246-1084
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> at home....
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to