I have a computer room with 3 lines of racks. Each rack line is
approximately 9 feet long and 3 feet wide. There is a 3 feet wide aisle
between each rack line (2 aisles). Each rack is approximately 6 feet in
height. Over each aisles, there is a lexan cover at 6-1/2 feet in height
above the floor and a door at either end of the aisle, making a "room" 15
feet long and 9 feet wide in the computer room. This is for rack air
conditioning. The computer room has a wet-pipe sprinkler system.
1. According to NFPA 101, the minimum headroom is 7 feet 6 inches. With the
door access, would this "room" be required to have a 7 feet 6 inches
ceiling?
2. To prevent sprinkler obstructions, would sprinklers be required in the
"room"?
Your opinions will be helpful.
 
Marshall Stout, P.E.
Fire Protection Engineer
Redstone Arsenal, AL
 
 