Thanks Craig.




<[EMAIL PROTECTED]>
Sent by:  [EMAIL PROTECTED]
08/26/2008 05:10 PM
Please respond to sprinklerforum

To
<[email protected]>
cc

Subject
RE: Computer room Racks with Blade Servers







I've done some queries but haven't got much to go on.  Basically due to 
tight controls there are few news worthy computer/control room fires. 
Those that do occur usually don't make the news just because they aren't 
all that dramatic.

http://www.highspringsherald.com/articles/2007/03/01/news/news05.txt


I THOUGHT THIS BOOK WAS INTERESTING.
http://cgi.ebay.com/Fire-in-the-Computer-Room-What-Now-Disaster-Recovery_W0QQitemZ290224079759QQcmdZViewItem




Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com

-----Original Message-----
From: [EMAIL PROTECTED] 
[mailto:[EMAIL PROTECTED] On Behalf Of 
[EMAIL PROTECTED]
Sent: Tuesday, August 26, 2008 9:18 AM
To: [email protected]
Subject: RE: Computer room Racks with Blade Servers

Craig,

Any specific documentation on actual fires?  We've gone through all the 
pros including as you've described.

I'm looking for a horror story - of course, one where no one was injured.

Thanks for the input.

Jim




<[EMAIL PROTECTED]>
Sent by:  [EMAIL PROTECTED]
08/26/2008 08:55 AM
Please respond to sprinklerforum

To
<[email protected]>
cc

Subject
RE: Computer room Racks with Blade Servers







We had similar discussions with a client on a very large automotive 
project.  The Underwriter was directing them to provide automatic 
sprinklers in the data center control rooms, they wanted nothing or at
best FM-200 alone.   The Underwriter had discussed business interruption
with them and asked them how long it would take to rebuild their computer 
control systems, programming, and the physical spaces and the owner 
replied it would probably take about 8 months to recreate their data 
center and get production back on line in the event of a catastrophic loss 
such as a fire.  At that time the owner's construction mgr. recalled 
another automotive project he was on several years back where the same 
protection approach was used, (smoke detectors and 2 hr construction) and 
that owner was offline for almost a year.  These are not just simple 
computer rooms as these rooms also control environmental systems, assembly 
automation as well as a myriad of other automatic functions.  They are the 
heart and brains of the site and without them the business is shut down.

Those two illustrations convinced the owner of our project that the risk 
was too great and they conceded to permit the installation of sprinklers 
in the rooms in conjunction with FM-200 and smoke detection.

The alternative was to construct a mirror site at another location that 
could be brought on-line almost immediately if needed in the event of a 
loss at the main control room.  This is an expensive proposition in 
comparison to adequate fire protection measures.

The scenario is a simple one, a sprinkler discharging 15-20 gpm or the 
fireman with a 100-200 gpm hose stream.  Which will result in more overall 
damage?  Down time of a few days or even weeks versus months to a year?
Which is preferred?



Roll the dice..................


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of 
[EMAIL PROTECTED]
Sent: Tuesday, August 26, 2008 8:29 AM
To: [email protected]
Subject: Re: Computer room Racks with Blade Servers

Marshall and fellow forumites:

Without knowing all the details , I would say that in most cases because 
the square footage is over 12,000 sq.ft. the IBC would require it.

The topic is very apropos to us at this time. We are in preliminary design 
of a foreign petrochemical facility, where our own automation and control 
people are adamantly opposed to providing even pre-action sprinkler 
protection in the control/computer rooms.  They claim that it is never 
done in the petrochem industry and that they don't want to be the first 
ones to try it. That country's building codes do not prohibit it. We have 
exhaustively pointed out all the advantages and disadvantages - property 
damage, business interruption potential, shutdown of operations, etc.
Unfortunately, they don't get that the odds of smoke detection and 
accidental operation of a sprinkler are astronomical. We have also given 
examples of not relying completely upon gaseous extinguishing due to doors 
propped open, future holes poked in walls, stuck dampers, loose ceiling 
tiles, etc.

I am not asking the forum for code references, statistical information on 
sprinkler system failures, reasons sprinklers should be provided, etc.
We've addressed all of that.  I would like to know of actual experiences 
anyone has on computer/control rooms suffering fire damage and shutting 
down operations - especially those that have only gaseous extinguishing.
Articles would be especially helpful.

I have personally witnessed an unsprinklered electrical room that 
completely burned and shutdown operations.  Unfortunately, these folks say 
it's apples and oranges.

Thanks in advance.

James L.(Jim) Roberts, PE/SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)





"Marshall Stout" <[EMAIL PROTECTED]> Sent by:
[EMAIL PROTECTED]
08/25/2008 07:49 PM
Please respond to sprinklerforum

To
<[email protected]>
cc

Subject
Computer room Racks with Blade Servers







I have a computer room with 3 lines of racks. Each rack line is 
approximately 9 feet long and 3 feet wide. There is a 3 feet wide aisle 
between each rack line (2 aisles). Each rack is approximately 6 feet in 
height. Over each aisles, there is a lexan cover at 6-1/2 feet in height 
above the floor and a door at either end of the aisle, making a "room" 15 
feet long and 9 feet wide in the computer room. This is for rack air 
conditioning. The computer room has a wet-pipe sprinkler system.
1. According to NFPA 101, the minimum headroom is 7 feet 6 inches. With 
the door access, would this "room" be required to have a 7 feet 6 inches 
ceiling?
2. To prevent sprinkler obstructions, would sprinklers be required in the 
"room"?
Your opinions will be helpful.

Marshall Stout, P.E.
Fire Protection Engineer
Redstone Arsenal, AL


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person or entity to 
which it is addressed and may contain proprietary, business-confidential 
and/or privileged material.
If you are not the intended recipient of this message you are hereby 
notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon this 
message is prohibited. If you received this in error, please contact the 
sender and delete the material from any computer.

Any views expressed in this message are those of the individual sender and 
may not necessarily reflect the views of the company.
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person or entity to 
which it is addressed and may contain proprietary, business-confidential 
and/or privileged material.
If you are not the intended recipient of this message you are hereby 
notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon this 
message is prohibited. If you received this in error, please contact the 
sender and delete the material from any computer.

Any views expressed in this message are those of the individual sender and 
may not necessarily reflect the views of the company.
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to