Marshall and fellow forumites:

Without knowing all the details , I would say that in most cases because 
the square footage is over 12,000 sq.ft. the IBC would require it.

The topic is very apropos to us at this time. We are in preliminary design 
of a foreign petrochemical facility, where our own automation and control 
people are adamantly opposed to providing even pre-action sprinkler 
protection in the control/computer rooms.  They claim that it is never 
done in the petrochem industry and that they don't want to be the first 
ones to try it. That country's building codes do not prohibit it. We have 
exhaustively pointed out all the advantages and disadvantages - property 
damage, business interruption potential, shutdown of operations, etc. 
Unfortunately, they don't get that the odds of smoke detection and 
accidental operation of a sprinkler are astronomical. We have also given 
examples of not relying completely upon gaseous extinguishing due to doors 
propped open, future holes poked in walls, stuck dampers, loose ceiling 
tiles, etc. 

I am not asking the forum for code references, statistical information on 
sprinkler system failures, reasons sprinklers should be provided, etc. 
We've addressed all of that.  I would like to know of actual experiences 
anyone has on computer/control rooms suffering fire damage and shutting 
down operations - especially those that have only gaseous extinguishing. 
Articles would be especially helpful.

I have personally witnessed an unsprinklered electrical room that 
completely burned and shutdown operations.  Unfortunately, these folks say 
it's apples and oranges. 

Thanks in advance.

James L.(Jim) Roberts, PE/SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)





"Marshall Stout" <[EMAIL PROTECTED]>
Sent by:  [EMAIL PROTECTED]
08/25/2008 07:49 PM
Please respond to sprinklerforum

To
<[email protected]>
cc

Subject
Computer room Racks with Blade Servers







I have a computer room with 3 lines of racks. Each rack line is
approximately 9 feet long and 3 feet wide. There is a 3 feet wide aisle
between each rack line (2 aisles). Each rack is approximately 6 feet in
height. Over each aisles, there is a lexan cover at 6-1/2 feet in height
above the floor and a door at either end of the aisle, making a "room" 15
feet long and 9 feet wide in the computer room. This is for rack air
conditioning. The computer room has a wet-pipe sprinkler system.
1. According to NFPA 101, the minimum headroom is 7 feet 6 inches. With 
the
door access, would this "room" be required to have a 7 feet 6 inches
ceiling?
2. To prevent sprinkler obstructions, would sprinklers be required in the
"room"?
Your opinions will be helpful.
 
Marshall Stout, P.E.
Fire Protection Engineer
Redstone Arsenal, AL
 
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to