NFPA 25 - 2002 Edition.
The way I read 12.1 and Table 12.1 applies to all valves, valve components and 
trim.
So yes check valves in the trim would need to be internally checked every 5 
years.

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov

** Note new email address: [EMAIL PROTECTED]


-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of MOWLE Kevin(K) - 
BRUCE POWER
Sent: Wednesday, August 27, 2008 10:36 AM
To: [email protected]
Subject: NFPA 25 section 13.4 System Valves




I have an inquiry re" NFPA 25 section 13.4 for "System Valves". The
paragraph for check valves, 13.4.2.2 specifies  a 5 year internal
inspection.

Unfortunately NFPA 25 section 3.5 does not include a definition of
"system valve" so this can lead to some interpretation problems.

As per NFPA 14, 6.4.2 a check valve is installed at the Fire department
connections which is tied directly to the main system header. As per
6.4.1 there is no isolation valve.  In one example here  the fire dept.
connection is tied directly to the main header so there is no means to
access this check valve short of a firewater system shutdown.

What about the small check valves on sprinkler, deluge and foam system
trim?  Are these considered "system valves"?

Are Class I and class III standpipe check valves considered "system
valves"?

thanks

Kevin Mowle
Bruce Power
Ontario, Canada
**************************************************************************************************
*** The contents of this email and any attachments
*** are confidential and may be privileged.
*** They are intended for the named recipient(s) only.
*** If this message has been delivered to you in error, please reply to the
*** sender to that effect, don?t forward the message to anyone
*** and delete the message from your computer.
*** Thanks for your help, and sorry for the inconvenience. (BP)
**************************************************************************************************

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to