Does anyone have a 13R handbook (I heard last year they were thinking of
doing one, but haven't seen anything yet.)

Question has arisen about the meaning of 6.8.2 Design Criteria outside of
the dwelling unit. Short version "Protect as per 13." AHJ says that means
protect the pool area using 3000 SF design area @ 0.10 and (Here's where we
differ seriously) Protect the attic wood truss space above.
I believe the intent is that the spaces that would be exempt from sprinkler
protection in 13R remain exempt, and only those areas which don't fit the
residential requirements of 13R must be protected by as if you were applying
13. So attics, crawl spaces and concealed combustible spaces remain
unprotected.
Is this how you all see it. (I even question the 3000 SF requirement,
because the spaces that drive the 3000 are outside the scope of 13R, and
therefore should not affect the areas of 13R that require 13 protection.)

Any ideas or comments appreciated.