It looks like we (NFPA) will be out of sequence with IBC forever. The
comment period for 2010 was over before any local AHJ adopted the 07. We
still have only one AHJ using 07. It's really hard to review a standard
for changes and ambiguities that we are not using on a day to day basis.
But that is an issue for a different thread.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris
Cahill
Sent: Tuesday, September 09, 2008 8:33 AM
To: [email protected]
Subject: RE: The sky is falling

You said "It seems like they are fixing something that isn't broke."

And this is unusual?  Seems like we fix more things that aren't broken
than
we fix things that are.  And I mean we because I am just as guilty in
not
sending in code changes or expressing comments on proposed code changes.


Sorry on the other issue, I can't spell sizmic brasing!

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [EMAIL PROTECTED]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Tuesday, September 09, 2008 9:39 AM
To: [email protected]
Subject: RE: The sky is falling

Thom,

Yeah I understand the reason for the cracked concrete, although I have
not heard of sprinkler systems falling to the floor in concrete
buildings. It seems like they are fixing something that isn't broke.

I don't know about the rest of the forum but this is a pretty big deal
for us. We are starting a 35 story post tension concrete high rise. The
Kwik Bolt requires about a 2.5" deep penetration so all the PT cables
are in danger. What are the odds of drilling 15,000 holes and not
hitting a cable. We are also starting a big twin tee parking garage. The
top of the tees is only 1.5" thick before the topping slab goes on.

Is anyone with a lot of experience with seismic bracing out there, Steve
Layton?

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Monday, September 08, 2008 4:10 PM
To: [email protected]
Subject: RE: The sky is falling

Ron:

You need to be a member of American Concrete institute to access all of
ACI
318-08, but their web site does say that there are changes expected to
the
08 document from the public comment period. The ICC web site also has it
For
Sale at
http://search.atomz.com/search/?sp-q=ACI+318-08&sp-a=00020177-sp00000000
&sp-
f=ISO-8859-1&sp-c=10&Search.x=9&Search.y=9
I have not read it however if my guess is right, the reason for cracked
concrete is that "It will be cracked after a seismic event, even if it
isn't
when you install the anchor" With that as a basis of design I would say
it
will apply to all hangers in a seismic structure. Sure hope someone from
Hangers and bracing steps up and fields this one.

But I've been wrong before!

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Monday, September 08, 2008 2:50 PM
To: [email protected]
Subject: RE: The sky is falling

Hi Thom,

Do you know if ACI 318-05 requires anchors be tested in cracked
concrete?
Hilti referenced ACI 318-08 as the driving force for testing anchors in
cracked concrete. I'm trying to find a copy ACI 318-05, the
05 edition is referenced by IBC 2006, so far no luck.

If this applies to seismic loads wouldn't we still be able to use HDI's
for
hangers and just use the TZ for EQB attachments?

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Monday, September 08, 2008 1:30 PM
To: [email protected]
Subject: RE: The sky is falling

Apparently this is driven by the 2006 IBC. The 2006 changed the system
of
testing for mechanical fasteners, you can check their (IBC) web site for
approved fasteners. This is mechanical fasteners only. The TZ has been
tested and approved. The 2006 has no criteria for testing Power driven
studs, and I believe says "Outside the scope" of this document or
outside
scope for seismic, something like that. Hilti has not tested the HDI or
HDI-P to the new criteria yet, so they are not approved by the building
code
where 2006 is applicable.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Monday, September 08, 2008 1:45 PM
To: [email protected]
Subject: The sky is falling

Anyone else out there heard from Hilti about no longer using their HDI
to
hang pipe from the bottom of cracked concrete in seismic categories C-F?
We
had a (the sky/pipe is falling) presentation from Hilti about using
their
new TZ Kwik Bolt instead of the HDI, HDI-P or powder drive pins. They
leave
you with the impression that all pipe supports must be changed to the
TZ,
they even sighted two projects in AZ where the contractors had to
abandon
the installed HDI's and reinstall the TZ.

I have been doing some research on their presentation and I don't think
their claims will stand the light of day but I would like some other
opinions. I would be glad to PM Hilti's power point presentation to any
interested parties.

I wonder if the marketing guru that got backflows required on Class 1 &
2 sprinkler systems went to work for Hilti?

Ron Fletcher
Aero Automatic
Phoenix, AZ
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)