The way that I have always done it was to try to get the effective
point of the test as close to the building as possible. The effective
point is the junction of flowing and non-flowing water. Often is
turns out to be the intersection of the hydrant spur with the main
line. There could be exceptions depending on the arrangement of the
hydrants and the lead in, but that would need to be looked at individually.
At 10:12 AM 9/23/2008, you wrote:
Content-Type: text/plain;
charset="us-ascii"
Content-Transfer-Encoding: 7bit
Content-Disposition:
O.K., can someone please help a dummy out (that would be me)? When looking
at a Civil Site Utility plan what method do you use to determine which
hydrant you want to flow and which one you put the gauge on? I've heard a
couple different ways, just wanted to get a popular opinion
Regards,
<http://www.firstdefensefire.com/>
E-mail message checked by Spyware Doctor (6.0.0.383)
Database version: 5.10760
http://www.pctools.com/en/spyware-doctor-antivirus/
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)