When I was at FM, that was the correct way to test a loop; flow one side, then the other, then both. However, most of the sprinkler designs were based on the flow of both. I don't understand the water company's logic unless there is a possibility that the loop could be modified, disconnected or impaired. Was the loop all on the property in question?

At 10:43 AM 9/23/2008, you wrote:
Todd.
I did a test the other day. The water purveyor insisted that we shut one of the control valves on the loop and test the hydrant furthest downsteam. The gauge hydrant was upsteam ofc the test hydrant.
The purveyor insisted that the loop should not be fully open.
Is that corect?  We were getting infp for a future system.
Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: Todd Williams - FPDC <[EMAIL PROTECTED]>

Date: Tue, 23 Sep 2008 10:38:39
To: <[email protected]>
Subject: Re: Flow Hydrant vs. Test Hydrant


The way that I have always done it was to try to get the effective
point of the test as close to the building as possible. The effective
point is the junction of flowing and non-flowing water. Often is
turns out to be the intersection of the hydrant spur with the main
line. There could be exceptions depending on the arrangement of the
hydrants and the lead in, but that would need to be looked at individually.



At 10:12 AM 9/23/2008, you wrote:
>Content-Type: text/plain;
>         charset="us-ascii"
>Content-Transfer-Encoding: 7bit
>Content-Disposition:
>
>O.K., can someone please help a dummy out (that would be me)? When looking
>at a Civil Site Utility plan what method do you use to determine which
>hydrant you want to flow and which one you put the gauge on?  I've heard a
>couple different ways, just wanted to get a popular opinion
>
>
>Regards,
>
>
><http://www.firstdefensefire.com/>
>
>
>
>
>
>
>
>
>E-mail message checked by Spyware Doctor (6.0.0.383)
>Database version: 5.10760
>http://www.pctools.com/en/spyware-doctor-antivirus/
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [EMAIL PROTECTED]
>
>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to