Well, what does the loop supply?   If other fire hydrants, is the AHJ
wanting the option to pump up the line to other apparatus or is the FDC
intended to serve just the sprinkler system(s)?   If the latter, then
you'll need an independent FDC's, separated from the loop by a check
valve, on each fire sprinkler lateral.   If the AHJ actually wants a
horizontal standpipe system, what you describe is functional, but not
preferred.   If there are no private hydrants, then the arrangement
sounds okay to me.

Steve Leyton
Protection Design & Consulting
San Diego, CA


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Tuesday, September 23, 2008 12:18 PM
To: [email protected]
Subject: UG FIRE LOOP - pumper connection

I have a job which has a 2000GPM fire pump supplied by a 12" city main.
The pump in turn feeds a 10" UG fire loop that runs around the building.
The FDC connection is located away from the building and connects to the
10" fire loop.  A fire hydrant supplied from the municipal water supply
is located next to the FDC.  So the pumper truck will hook up to the
municipal hydrant and pump into the FDC for the UG loop.  Do you see any
potential problems with a pumper truck, rated for 1700 GPM, pumping into
a fire loop supplied by a 2000GPM fire pump?  
Thanks,
Dewayne
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 3466 (20080923) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 3466 (20080923) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to