You mean you "received applications for "limited area window
protection", "13R window protection" and so forth" for exterior window
applications? That's fine but the WS for the application Russ is talking
about is not an exterior application. There should be no reason the WS
heads couldn't be used in an otherwise unsprinklered building. It passed the
same test as every other 2 hr rated wall listed in the UL directory.
The cut sheet supports this in "Based on this successful testing, the
Model WS Specific Application Window Sprinkler can be used as interior
protection of windows or glazing in a sprinklered building or
non-sprinklered building."
I just wanted to be clear your rejection seems appropriate for exterior
applications because of the specific language in 704.12 but a rejection
would not be expected in an interior application where 2 hr sheetrock wall
would be acceptable with or without a building sprinkler.
Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
763-658-4483
763-658-4921 fax
Email: [EMAIL PROTECTED]
Mail: P.O. Box 69
Waverly, MN 55390
Location: 4439 Hwy 12 SW
Waverly, MN 55390
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John Drucker
Sent: Wednesday, October 01, 2008 1:44 PM
To: [email protected]
Subject: FW: Window Sprinklers
Guys,
Its important to note that 2006 IBC 704.12 Exception requires that the
building is protected throughout by an automatic sprinkler system in
accordance with NFPA-13.
That's really big. I've received applications for "limited area window
protection", "13R window protection" and so forth and that's simply not
permitted. In order to use the exception at 704.12 a complete NFPA-13
(2002) sprinkler system must be provided.
John Drucker
Fire Protection Subcode Official (AHJ)
Red Bank, NJ
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Wednesday, October 01, 2008 11:42 AM
To: [email protected]
Subject: RE: Window Sprinklers
2006 IBC 704.12 provides for exterior window opening utilizing a water
curtain. "Exception - Opening protectives are not required where the
building is protected throughout by an automatic sprinkler system and
the exterior openings are protected by an approved water curtain using
automatic sprinklers approved for that use." The sprinklers and the
water curtain shall be installed in accordance with section 903.3.1.1
(NFPA13) and shall have an automatic water supply and fire department
connection."
The Tyco/Central WS for example is a listed window sprinkler. ICC ES
Legacy Report NER-516 provides specific instructions on the application
of window sprinklers including but not limited glazing, frames, non
bearing walls, etc. The complete report can be downloaded/read at;
http://www.icc-es.org/reports/pdf_files/NES/NER516.pdf
John Drucker
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Wednesday, October 01, 2008 10:28 AM
To: [email protected]
Subject: RE: Window Sprinklers
The window sprinkler was tested using the exact same criteria as is used
to establish any other rated assembly. A test fire is built on one
side of the subject and burned for the duration of the rating and then
there's a steady-stream hose test (not entirely sure if that's of the
same duration - Drucker, chime in now please) during which water is
jetted against the subject and it can't fail. I think your assumption
is correct that the surface is protected so long as the sprinkler(s)
flow at their minimum required rate - 15 or 20 GPM depending on spacing.
Steve Leyton
Protection Design & Consulting
San Diego, CA
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, October 01, 2008 6:43 AM
To: [email protected]
Subject: RE: Window Sprinklers
Just a guess but I think the window damage (without the sprinkler
protection) would occur within the first minutes. Once the minimum
water discharge is established I would assume the protection would last
as long as the water is flowing. Does this sound logical?
Bill Brooks
William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell
-------- Original Message --------
Subject: RE: Window Sprinklers
From: "Bill Minkel" <[EMAIL PROTECTED]>
Date: Wed, October 01, 2008 9:27 am
To: <[email protected]>
Ahhhhh, Gotcha
Bill Minkel, Designer
Dallas, TX
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Tuesday, September 30, 2008 3:16 PM
To: [email protected]
Subject: RE: Window Sprinklers
Of course it's MORE than adequate for a 1 hr wall, the question was is
there a "Less" that would work for 1 hr, but not 2 hr? Maybe a smaller
orifice or totally different head or even a vert. sidewall? Hence
"Window Sprinkler Lite"
Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill
Minkel
Sent: Tuesday, September 30, 2008 11:29 AM
To: [email protected]
Subject: RE: Window Sprinklers
Educate me here, I would have thought that a wall assembly rated for 2
hours would also be more than adequate for 1 hour?
Bill Minkel,
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
__________ Information from ESET NOD32 Antivirus, version of virus
signature database 3485 (20081001) __________
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com
__________ Information from ESET NOD32 Antivirus, version of virus
signature database 3485 (20081001) __________
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)