Everything you need to know is in the ICC Legacy report including why you need 
a pony wall.


 

Rahe Loftin



----- Original Message -----
From: "Cliff Whitfield" [[email protected]]
Sent: 03/21/2009 05:04 PM EST
To: <[email protected]>
Subject: RE: Window Sprinklers



Thom,

Great info.  Thanks.

Cliff
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Saturday, March 21, 2009 4:00 PM
To: [email protected]
Subject: RE: Window Sprinklers

There is a test white paper on these heads on the ICC web site, that I
looked at several years ago. Basically these heads are to keep the glass
from reaching a temp that would cause it to crack or fail. That temp is
higher than the rating for these heads. The heads are exposed to the same
heat sources as are the glass, Convection conduction and radiant heat. They
don't need to activate at all if the fire is controlled by the control mode
sprinklers, but they need to operate if the sprinkler system is overwhelmed
or the fire source is located close to the glass. They need to maintain the
hour rating of the separation. Both sides of the glass is the preferred
installation unless you can guarantee which side will have the fire. As you
know the convection will not usually be a large factor with windows this far
below the ceilings, but radiant heat and conduction, as well as heat forced
down by the ceiling sprinklers when they operate can put the glass at risk.
Timely is relative. They only need to activate before the glass fails, or
gets hot enough for the water to cause the glass to fail. That is why the
placement rules are so specific. 

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Cliff
Whitfield
Sent: Saturday, March 21, 2009 11:58 AM
To: [email protected]
Subject: RE: Window Sprinklers

Thom,

That brings up another issue I've been wondering about.  I am being required
to use these on both sides of the windows.  I have not studied the details
yet but if the top of the window is at 7' AFF and the ceiling is at 12', how
do the heads activate in a timely fashion?  That could be an issue on the
inside of this area.  

The bigger problem I have is that this window (about 140 lf in one
direction) is for an overlook into a restoration hangar and the roof on the
outside of the window is probably 20' above the top of the window.  What is
the chance that those heads will ever activate?  I'm sure the guys at Tyco
did their research and the EoR knows exactly what he is doing but something
in my mind wants to throw up a red flag.  It just goes against what I think
I understand about sprinklers. 

Cliff


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to