Thank You, one and all! Got what I needed. Sure do enjoy monitoring this site and I pick up goodies all the time. I will make an effort to do San Diego next year, mainly to find out what happens at George's Room.

----- Original Message ----- From: "George Church" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, October 24, 2008 1:09 PM
Subject: RE: Pitot Chart


From Denise at hydro flow:

Here are the pitot formula and coefficients for all sizes of the Hose
Monsters and Nozzle Inserts.

    Q = 29.83 * √P * D2 * Coefficient
    Where Q = flow rate in GPM, P = pitot pressure, D = nozzle diameter

Product Coefficient
Nozzle Insert 1 1/8” 0.99
Nozzle Insert 1 ¾” 0.975
Hose Monster 2 ½” 0.906

    The 4” and 4 ½” Hose Monsters actually use a different formula
because they are not using a pitot, but these numbers work for the above
pitot formula.
    Product Coefficient
    Hose Monster 4” 0.71159
    Hose Monster 4 ½” 0.54816

The Pitotless Nozzles are different also.

Links to flow charts for low, "normal" and high pressures:
http://www.hosemonster.com/downloads/FCHM2H.pdf
http://www.hosemonster.com/downloads/FCHM2HLP.pdf
http://www.hosemonster.com/downloads/FCHM2HHP.pdf
* * * *
Obviously, the chart is pretty darn convenient when you're in the field;
rather than use a calculator when I've gone out without the chart, I just
use my cel to call the office and ask someone for the GPM for my pitot
pressure.

Saw the pitotless nozzles last week at AFSA- pretty neat. They've come a
long way!

TGIF
glc

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:sprinklerforum-
[EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC
Sent: Friday, October 24, 2008 2:35 PM
To: [email protected]
Subject: Re: Pitot Chart

Dennis,

Why would the pitot have a chart? Is this actually a diffuser or
nozzle with a built-in pitot?

What I did with my Hose Monster was to use the chart and calc
backwards to come up with the K factor, then I wrote it on the HM
with a permanent marker. That way, if I lose the chart, oh well.


At 02:10 PM 10/24/2008, you wrote:
I have a "Sierra"  brand Pitot I bought circa 1990 and my Fitter
lost the chart yesterday while doing a flow test. I think it is the
very similar to the one listed in the Potter Roemer catalogue. I was
hoping someone could email or fax me a copy? Hate to buy a new one
over the chart. Thanks in advance.
Fax 541 245 0498
Phone    245 0466


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


--------------------------------------------------------------------------------



No virus found in this incoming message.
Checked by AVG - http://www.avg.com
Version: 8.0.175 / Virus Database: 270.8.2/1742 - Release Date: 10/23/2008 3:29 PM

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to