My understanding is that there was no test requiring more than 6 or 7 heads.


If 7 heads did not suppressed the fire, 12 head would not either. The next
stage is 20 or 25 maybe operating in control mode. 

Hence, if my understanding prevails than 14 head are no better than 12
heads. 

If anybody has other information I will appreciate that and I will update my
data base.

Now,  the question is where in the NFPA-13 ver. 2007 it is stating that you
need to add 2 heads to the ceiling 14 heads. 

Dan

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: 05 November, 2008 11:19 AM
To: [email protected]
Subject: RE: ESFR Heads below obstructions

Dan-
You could flow more than 12 at the roof in order to flow the required
minimum MRA. You could be adding 2 more below obstructions. You could flow
more than those 15 if the insurance or other AHJ directs you to.

Only thing more serious than the % impact you mention would be NOT having it
when you need it. Those fire videos James includes in his seminars certainly
make a memorable example of howcuz ya need all that water, and what happens
if ya don't. can you spell free burn?

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of danarbel
Sent: Wednesday, November 05, 2008 2:40 AM
To: [email protected]
Subject: RE: ESFR Heads below obstructions

Ken,
Getting through all the quotes below I still don't see a statement that the
2 head below obstruction are added to the 12 heads required under the high
level. 

In addition, all the clauses you quote say essentially the same thing, that
2 heads should be included in the calc.  Namely, why not taking 10 heads in
the higher level + 2 heads from the lower level. 

In my humble mind,  adding 2 heads is not logical.  Normally the hot gases
will bypass the lower level heads.  If they are initiated, it means that the
gas jet hits the head from below. This is very good since this head initiats
just above the source of this hot jet. Maybe in this case one head will do
the job. 

So, again, according to my humble mind, operation of heads under lower
obstruction have a positive effect. You will need less higher level heads
initiations. 

I would appreciate any opinions including negative ones to my opinion. 

Adding 2 heads is 17% more flow, 36% more pressure loss. 

This is very serious. 

Dan 

 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: 05 November, 2008 12:15 AM
To: [email protected]
Subject: RE: ESFR Heads below obstructions

Yeah,

12 above (four sprinks on three branch lines), minimum design area of 960
sq. ft., plus when installed above and below obstructions include discharge
for two additional sprinklers for one of the other levels.  (NFPA 13, 2002,
12.3.2.3.3 & 12.3.2.3.4)

12+2=14.  Yup that's why I got.

Did have to take the shoes off to verify that data, so we should be good to
go.


Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack,
SET
Sent: Tuesday, November 04, 2008 5:03 PM
To: [email protected]
Subject: RE: ESFR Heads below obstructions

It must be the election that is frying our brains.  I read all of that and
see you need 12 at the roof, plus up to 2 below the obstruction for a max of
14 ESFR sprinklers.  What say everyone?

T-Mack

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of danarbel
Sent: Tuesday, November 04, 2008 2:48 PM
To: [email protected]
Subject: RE: ESFR Heads below obstructions

Well, I read all that and it seems that all you need are 12 heads

Dan


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: 04 November, 2008 7:28 PM
To: [email protected]
Subject: ESFR Heads below obstructions

Dan,

All references here are from the '07 edition of NFPA-13:

14.4.4 Where ESFR sprinklers are installed above and below obstructions, the
discharge for up to two sprinklers for one of the levels shall be included
with those of the other level in the hydraulic calculations.

15.4.4 Where ESFR sprinklers are installed above and below obstructions, the
discharge for up to two sprinklers for one of  the levels shall be included
with those of the other level in the hydraulic calculations.

16.2.3.5 Where ESFR sprinklers are installed above and below obstructions,
the discharge for up to two sprinklers for one of the levels shall be
included with those of the other level in the hydraulic calculations

16.3.3.6 Where ESFR sprinklers are installed above and below obstructions,
the discharge for up to two sprinklers for one of the levels shall be
included with those of the other level in the hydraulic calculations.

17.2.3.4 Where ESFR sprinklers are installed above and below obstructions,
the discharge for up to two sprinklers for one of the levels shall be
included with those of the other level in the hydraulic calculations.

17.3.3.5 Where ESFR sprinklers are installed above and below obstructions,
the discharge for up to two sprinklers for one of the levels shall be
included with those of the other level in the hydraulic calculations.

22.4.4.6.4 The requirements of 22.4.4.6.1 to include every sprinkler in the
design area to be included in the system discharge shall not apply; where
ESFR sprinklers are installed above and below obstructions, the discharge
for up to two sprinklers from one of the levels shall be included with those
of the other level in the hydraulic calculation.

Based on what I read in the ROP just published it doesn't look like any of
these have been removed, although it appears that the wording in
22.4.4.6.4 has been moved around a bit, and a new 22.4.4.6.4.1 has been
added (See 13-462, Log CP82 in the ROP)

Hope that is what you were after.
*
*PARSLEY CONSULTING

Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website



danarbel wrote:
> Question regarding the number of ESFR heads required for hydraulic calc.
>
> The nominal number is 12.
>
> There was a requirement to add 2 heads if there are heads installed
> below beams or AC ducts.
>
> If I'm not wrong the addition of 2 heads was abolished.
>
> Please confirm or correct me,
>
> Dan Arbel
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [EMAIL PROTECTED]
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> No virus found in this incoming message.
> Checked by AVG - http://www.avg.com
> Version: 8.0.138 / Virus Database: 270.8.6/1765 - Release Date:
> 11/3/2008
4:59 PM
>
>
>
>
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


__________ NOD32 3580 (20081103) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

__________ NOD32 3583 (20081104) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


__________ NOD32 3580 (20081103) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


__________ NOD32 3580 (20081103) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to