Dan,
All references here are from the '07 edition of NFPA-13:
14.4.4 Where ESFR sprinklers are installed above and below obstructions,
the discharge for up to two sprinklers for one of the levels shall be
included with those of the other level in the hydraulic calculations.
15.4.4 Where ESFR sprinklers are installed above and below obstructions,
the discharge for up to two sprinklers for one of the levels shall be
included with those of the other level in the hydraulic calculations.
16.2.3.5 Where ESFR sprinklers are installed above and below
obstructions, the discharge for up to two sprinklers for one of the
levels shall be included with those of the other level in the hydraulic
calculations
16.3.3.6 Where ESFR sprinklers are installed above and below
obstructions, the discharge for up to two sprinklers for one of the
levels shall be included with those of the other level in the hydraulic
calculations.
17.2.3.4 Where ESFR sprinklers are installed above and below
obstructions, the discharge for up to two sprinklers for one of the
levels shall be included with those of the other level in the hydraulic
calculations.
17.3.3.5 Where ESFR sprinklers are installed above and below
obstructions, the discharge for up to two sprinklers for one of the
levels shall be included with those of the other level in the hydraulic
calculations.
22.4.4.6.4 The requirements of 22.4.4.6.1 to include every sprinkler in
the design area to be included in the system discharge shall not apply;
where ESFR sprinklers are installed above and below obstructions, the
discharge for up to two sprinklers from one of the levels shall be
included with those of the other level in the hydraulic calculation.
Based on what I read in the ROP just published it doesn't look like any
of these have been removed, although it appears that the wording in
22.4.4.6.4 has been moved around a bit, and a new 22.4.4.6.4.1 has been
added (See 13-462, Log CP82 in the ROP)
Hope that is what you were after.
*
*PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
danarbel wrote:
Question regarding the number of ESFR heads required for hydraulic calc.
The nominal number is 12.
There was a requirement to add 2 heads if there are heads installed below
beams or AC ducts.
If I'm not wrong the addition of 2 heads was abolished.
Please confirm or correct me,
Dan Arbel
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
No virus found in this incoming message.
Checked by AVG - http://www.avg.com
Version: 8.0.138 / Virus Database: 270.8.6/1765 - Release Date: 11/3/2008 4:59 PM
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)