The following is from NFPA 20, 2007:

5.14.3 Suction Size.
5.14.3.1 Unless the requirements of 5.14.3.2 are met, the size of the
suction pipe for a single pump or of the suction header pipe for multiple
pumps (operating together) shall be such that, with all pumps operating at
150 percent of rated capacity, the gauge pressure at the pump suction
flanges shall be 0 psi (0 bar) or higher.
5.14.3.2 The requirements of 5.14.3.1 shall not apply where the supply is a
suction tank with its base at or above the same elevation as the pump, where
the gauge pressure at the pump suction flange shall be permitted to drop to
-3 psi (-0.2 bar) with the lowest water level after the maximum system
demand and duration have been supplied.
5.14.3.3 The suction pipe shall be sized such that, with the pump(s)
operating at 150 percent of rated capacity, the velocity in that portion of
the suction pipe located within 10 pipe diameters upstream of the pump
suction flange does not exceed 15 ft/sec (4.57 m/sec).
5.14.3.4 The size of that portion of the suction pipe located within 10 pipe
diameters upstream of the pump suction flange shall be not less than that
specified in Section 5.25.

To re-cap, the sprinkler system demand is 222 gpm @ 40 psi. The fire pump
installed is 400 gpm @ 70 psi. The water supply is tanks installed with
centre of outlet flanges 22 inches BELOW the centre of pump suction flange.

Question #1: Will 5.14.3.2 apply? It says "...suction tank with its base at
or above the same elevation as the pump, ...". Elevation of what part of the
pump?

Assuming it applies and the pressure at the pump suction flange is permitted
to drop to -3 psi at the lowest water level,

Question #2: Section 5.14.3.2 "...after the maximum system demand and
duration have been supplied." So will the -3 psi be the static head and
friction loss when flowing the maximum system demand (in this case 222 gpm?
Not 150% of the rated capacity?

Tony 