The following is from NFPA 20, 2007: 5.14.3 Suction Size. 5.14.3.1 Unless the requirements of 5.14.3.2 are met, the size of the suction pipe for a single pump or of the suction header pipe for multiple pumps (operating together) shall be such that, with all pumps operating at 150 percent of rated capacity, the gauge pressure at the pump suction flanges shall be 0 psi (0 bar) or higher. 5.14.3.2 The requirements of 5.14.3.1 shall not apply where the supply is a suction tank with its base at or above the same elevation as the pump, where the gauge pressure at the pump suction flange shall be permitted to drop to -3 psi (-0.2 bar) with the lowest water level after the maximum system demand and duration have been supplied. 5.14.3.3 The suction pipe shall be sized such that, with the pump(s) operating at 150 percent of rated capacity, the velocity in that portion of the suction pipe located within 10 pipe diameters upstream of the pump suction flange does not exceed 15 ft/sec (4.57 m/sec). 5.14.3.4 The size of that portion of the suction pipe located within 10 pipe diameters upstream of the pump suction flange shall be not less than that specified in Section 5.25.
To re-cap, the sprinkler system demand is 222 gpm @ 40 psi. The fire pump installed is 400 gpm @ 70 psi. The water supply is tanks installed with centre of outlet flanges 22 inches BELOW the centre of pump suction flange. Question #1: Will 5.14.3.2 apply? It says "...suction tank with its base at or above the same elevation as the pump, ...". Elevation of what part of the pump? Assuming it applies and the pressure at the pump suction flange is permitted to drop to -3 psi at the lowest water level, Question #2: Section 5.14.3.2 "...after the maximum system demand and duration have been supplied." So will the -3 psi be the static head and friction loss when flowing the maximum system demand (in this case 222 gpm? Not 150% of the rated capacity? Tony _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)