Ed, thanks for replying. Regarding question #1. The base of the tank (not
tank outlet) in 99% of applications will be below the centreline of the pump
suction. So the applicable section is 5.14.3.1 as 5.14.3.2 will not apply?

Hope someone from the 20 committee will shed some light, unofficially.

Tony 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: November 10, 2008 9:26 AM
To: [email protected]
Subject: RE: Fire Pump Suction -part 2

> Question #1: Will 5.14.3.2 apply? It says "...suction tank with its 
> base at or above the same elevation as the pump, ...". Elevation of 
> what part of the pump?

Without more clarification from NFPA 20, I'd assume it means the centerline
of the suction.  Maybe someone on the 20 committee would care to comment
(unofficially, of course). 


> Question #2: Section 5.14.3.2 "...after the maximum system demand and 
> duration have been supplied." So will the -3 psi be the static head 
> and friction loss when flowing the maximum system demand (in this case 
> 222 gpm?
> Not 150% of the rated capacity?
> 
> Tony


I think section 5.14.3.2 means the pressure at the pump suction can't be
less than -3 psi while flowing 150% of it rated capacity after the water
level in the tank has been drained down by its required capacity.  In other
words, it the tank is required to have a capacity of 4,500 gallon (a made-up
number), it would be the water level in the tank after 4,500 gallon have
been sucked out.  This water level would give the minimum static head.  I
lean toward the 150% of rated pump capacity because all other references in
5.14.3 are to 150%.  Again, maybe someone on the 20 committee would care to
comment.

Ed Kramer
Littleton, CO

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to