> Question #1: Will 5.14.3.2 apply? It says "...suction tank with its base > at > or above the same elevation as the pump, ...". Elevation of what part of > the > pump?
Without more clarification from NFPA 20, I'd assume it means the centerline of the suction. Maybe someone on the 20 committee would care to comment (unofficially, of course). > Question #2: Section 5.14.3.2 "...after the maximum system demand and > duration have been supplied." So will the -3 psi be the static head and > friction loss when flowing the maximum system demand (in this case 222 > gpm? > Not 150% of the rated capacity? > > Tony I think section 5.14.3.2 means the pressure at the pump suction can't be less than -3 psi while flowing 150% of it rated capacity after the water level in the tank has been drained down by its required capacity. In other words, it the tank is required to have a capacity of 4,500 gallon (a made-up number), it would be the water level in the tank after 4,500 gallon have been sucked out. This water level would give the minimum static head. I lean toward the 150% of rated pump capacity because all other references in 5.14.3 are to 150%. Again, maybe someone on the 20 committee would care to comment. Ed Kramer Littleton, CO _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)