> Question #1: Will 5.14.3.2 apply? It says "...suction tank with its base
> at
> or above the same elevation as the pump, ...". Elevation of what part of
> the
> pump?

Without more clarification from NFPA 20, I'd assume it means the centerline
of the suction.  Maybe someone on the 20 committee would care to comment
(unofficially, of course). 


> Question #2: Section 5.14.3.2 "...after the maximum system demand and
> duration have been supplied." So will the -3 psi be the static head and
> friction loss when flowing the maximum system demand (in this case 222
> gpm?
> Not 150% of the rated capacity?
> 
> Tony


I think section 5.14.3.2 means the pressure at the pump suction can't be
less than -3 psi while flowing 150% of it rated capacity after the water
level in the tank has been drained down by its required capacity.  In other
words, it the tank is required to have a capacity of 4,500 gallon (a made-up
number), it would be the water level in the tank after 4,500 gallon have
been sucked out.  This water level would give the minimum static head.  I
lean toward the 150% of rated pump capacity because all other references in
5.14.3 are to 150%.  Again, maybe someone on the 20 committee would care to
comment.

Ed Kramer
Littleton, CO