Fellow forumites,

The discussions have been interesting.  Despite the commercials, no one 
size fits all. I offer the following, some of which has already been 
mentioned.

In many of the larger engineering firms and for very large projects, 
ideally all disciplines will have their work in the 3-D model.  At Fluor, 
most disciplines provide 2-D drawings showing dimensions, elevations, etc. 
 However, that is not true for process piping.  Piping rarely provides 
orthographics.  Their finished products are ISO drawings, which are used 
for shop or on-site fabrication of spools ( configurations of piping, 
fittings, valves, and instrument assemblies) and installation.

Many of the bigger firms, Fluor, Bechtel, CH2MHill, Jacobs, etc. use 
Intergraph PDS. 

Our FP designers and engineers design as they're modeling and vice-versa. 
Because PDS* is not specifically intended for fire protection systems and 
not set up for sizing hydraulically, we usually model mains as 6 inch and 
branch lines as 2 inch primarily for space allocation. We also model 
sprinklers.  We "extract" the 2-D from the model to create drawings with 
sizes to be modified according to hydraulic calculations. Due to time 
constraints, we generally don't go back into the model to change sizes. 
The approach works well provided that all disciplines reference others to 
avoid conflicts.  Additionally, clash reports are generated on a regular 
basis to hopefully keep interferences from getting out of control.  This 
works especially well where the project engineer assigns horizontal 
lanes/envelopes to disciplines and enforces them.  Sadly, this is not 
frequent, so it's a situation of who claims they were there first. 

Prior to anything being constructed, the 3-D model is supposed to be 
interference free and usually is. 

The sprinkler drawings we create are included in the sprinkler system 
installation bid packages.  If the successful sprinkler contractor does 
not have the ability to convert from Microstation to AutoCad, we will do 
that.  The contractors are able to create fabrication drawings directly 
from our drawings.  Because the systems are coordinated, the sprinkler 
contractor's directive is exactly follow the drawings.  The construction 
folks generally hold the various contractors to the drawings.  In my 
opinion, if an HVAC contractor shifts his duct 6" and causes an 
interference, whoever he hits has a legitimate beef and possible change 
order.

Small conduits are not modeled, but the electrical contractors that they 
must defer to what is modeled and coordinate their work with a model 
review terminal on site.

Even at Fluor, it's a continual process to make sure we are provided with 
engineering/design/modeling hours, but we're in much better shape than we 
used to be.  I'm definitely not claiming that we have the problem licked - 
it took years to get to this stage.

I have never gotten bids as close as Craig mentioned, but we get 
reasonably close bids where we have provided a detailed set of drawings. 
Of course, there is sometimes the lone bidder, who is so busy he/she 
throws out a high number just to see if it sticks.  If does that's a 
worthwhile problem to resolve.

Regards,

James L.(Jim) Roberts, PE/SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)

*We have AutoSprink licenses, but seamlessly working with PDS is not what 
it should be.





<[EMAIL PROTECTED]>
Sent by:  [EMAIL PROTECTED]
11/12/2008 11:54 AM
Please respond to sprinklerforum

To
<[email protected]>
cc

Subject
RE: design and coordination roles and responsibilites.







Well if you want to be innovative then by all means be so.  On projects 
such as this if the contractor has a better idea, I'm all for it and then 
we will sit down and see how it will integrate into the overall picture. 
But if there was no direction given on projects like this where there's 
20lbs stuffed in the 10lb bag, guess who will be the loser every time, you 
guessed it boys and girls, the sprinkler contractor.

So if you get innovative and there's extremely limited space and you 
venture off on your own, get ready to install it and reinstall it more 
than once, at your expense.  Did you coordinate like the specs directed 
you?

The problem with a lot of AE firms is even IF they do have competent 
design/3D modeling persons, they can't coordinate with something that 
isn't there.  If it's not in the model, it doesn't exist is pretty much 
the normal viewpoint.  So if you're not part of that effort, you're on 
your own.  Hope you bid high enough.

Fire protection is always treated as the "red-head step child" in the 
engineering world.  To most people fire protection is a waste of money, it 
makes no profit, is expensive and takes up valuable space, then it becomes 
a life-long maintenance headache.  So any time we can get it recognized as 
being a vital discipline and building system and included in any level of 
detail in the overall project design, I'll take it.

We're just trying to put a better product on the streets than the typical 
big "X" on the drawing whenever possible to make the more complex projects 
flow better.  Hopefully at the end of it all everybody goes home with a 
few more bucks in their pocket and a positive experience, instead of 
saying "OH $%^&* I wish we had never taken that job!"

Oh and I know that ALL disciplines have been engineering in 3D since the 
beginning of time.

Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-----Original Message-----
From: [EMAIL PROTECTED] 
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, 
Ron
Sent: Tuesday, November 11, 2008 1:14 PM
To: [email protected]
Subject: RE: White papers and definition of roles

Right on George. With all the special systems I would expect more than $2k 
difference in the specialty equipment quotes and the prices should be 
closer if you take away the opportunity for innovation of design by the 
bidders.

Our prices are higher on jobs requiring 3D or BIM. We find there is very 
little coordination and more "here is where we are so now you
(sprinkler) can go around us. It's like a 3D retrofit. The only thing that 
changes is we spend more design time to come up with the same product. 
Besides we FP contractors have been doing 3D since the beginning of time, 
it's just that the presentation has been 2D.

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George 
Church
Sent: Tuesday, November 11, 2008 7:00 AM
To: [email protected]
Subject: RE: White papers and definition of roles

Ummm, maybe the two bidders had breakfast together on bid morning?
Don't throw your elbow out patting yourself on the back.

Coincidence or a comp price is far more likely to produce bids within 
.001% of each other than quality of the bid documents.

Seriously, if you'd given em a stocklist, a finished, coordinated dwg, and 
a rational schedule, there'd be more difference in the price than this 
just on how different companies allocate OH, backlog needs, lift pricing 
renting vrs owning, mileage from office to site variance, mix of each 
contractor's design talent pool $ cost, workman's comp experience 
reflected in what could be drastically different rates, skill of the two 
estimators, whether someone got something last night- There are so many 
variables, I'd suspect a comp number before a headless piping layout as 
the root cause for the close resemblance.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of 
[EMAIL PROTECTED]
Sent: Tuesday, November 11, 2008 8:46 AM
To: [email protected]
Subject: RE: White papers and definition of roles

Speaking of bid prices.  We performed our first AutoCAD based 3D 
integration of fire protection on a recent project.  Our typical corporate 
deliverable is the design criteria and a floor plan with equipment on it. 
(I have had a couple complete installation level design requests but they 
are rare in this
industry)  Typical criteria based design, no piping, or heads or anything 
else.  (because the contractor will do it for free).  Anyway,  as we've 
progressed into the 3D realm I've pushed to get fire protection included 
in the 3D modeling.  Convincing the powers that be that by at least 
including mains and branch lines into the model and coordinating their 
locations and elevations will aid the contractor during installation, 
reduce his design time and reduce change orders and bring us tighter bids 
as there is less for the imagination and more solid information to work 
with.

So they let us do the piping layout but no heads, so we did the layout in 
the model dealing with equipment, steel and other modeled obstructions.


Two weeks ago the project went out for bids.  We had 3 bidders.  One 
dropped out due to various personal reasons but the bids came back 
yesterday from the other two.

The fire protection bids on the project were within $2,000 of each other.
Now that may not sound like a big deal but understand the total above 
ground fire protection is valued at almost $1.5 million dollars.

For two bidders to be that close is pretty unusual.  But it validated the 
need for better design other than the old floor plan with the note "follow 
NFPA 13" and similar stuff.

Hopefully we can continue this trend within our company.  I know this 
would be difficult for many companies because there is a lack of qualified 
people who can actually layout a fire protection system and this project 
ran the gamut of system types from wet, dry, pre-action, foam-water 
deluge, low expansion foam, dry chemical, CO2 and a proprietary, IR 
triggered, high
speed, deluge curtain system (that is really cool by the way).

Now I'm hoping that our management sees the value in this effort and will 
continue down this path.  Convincing some to allow us to provide more than 
the bare minimum of fire protection information is a tough fight.  For 
whatever reason is has been for years.  Maybe it has to do with the lack 
of qualified people, some of it is based on economics, some of it is 
perceived value, like I said, most AE firms feel the contractor provides 
the engineering effort for free so why do anything other than a spec and 
some fancy notes.

I actually had one PM complain that the sprinkler contractors ALWAYS put 
their pipe in the wrong place and it has to be torn down and removed.
He
caught me on a good day so I graciously (stop snickering)  reminded him of 
the directive we typically give sprinkler contractors:  1. coordinate with 
everyone and everything.  But at the same time all we give them is a floor 
plan of the building, no process piping layouts (because there is no such 
animal), no steel plans, no duct layouts, etc.  So how can he coordinate 
with things that don't exist or haven't been designed yet?  Hence my sales 
pitch for getting it in the model and then giving that info to the 
contractor.

But this is one I will put in the WIN column.  They come far and few 
between so forgive me while I savor the moment....................




Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark 
Sornsin
Sent: Monday, November 10, 2008 6:16 PM
To: '[email protected]'
Subject: RE: White papers and definition of roles

Then there are those jurisdictions such as ND where you not only don't get 
registered in a specific discipline, but complaints will not be 
investigated unless there is a problem with the design. E.g., simply being 
trained in structural engineering and signing someone's sprinkler system 
design is not a problem that will be investigated.  It may violate the 
engineers' code of ethics, but it won't see action from the State Board 
unless there arises some issue with the design. So if you're a PE not 
trained in sprinkler design, just get some non-PE designer to complete the 
work and then you can seal it. Effectively there is no problem.  If the 
building burns as a result of improper design, then you've got a problem.

Of course, how many MEs even attempt to design a system?  It's pretty 
difficult to hold an engineer to the fire when his "design" boils down to 
"do it per code." I have had MEs ask me why I would ever attempt to 
provide a complete sprinkler system design.  They wonder, "doesn't that 
expose you to more liability?" Gee, and here I thought design and the 
associated liability was the whole point of our profession.

But that leads us right back to Thom's point about doing whatever is 
easiest.  And when an ME gets paid on a percentage of construction, 
there's no sense putting time into a project and exposing himself to more 
liability.
Besides, his lack of effort will typically result in higher bid prices and 
therefore higher fees.  And the contractors don't want to rock the boat 
because the engineer may make their life more difficult. So the cycle 
continues.

I ought to write an article...

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104-7079

[EMAIL PROTECTED]

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to