And the flip side to that is that you have two connections within a
half-flight of the fire floor.  If the first connection should fail, or
if additional attack lines are required, you can pull as many as four
small lines without having to turn the hoses.   I've always preferred
the floor landing location because here in warm-weather country we
always use wet standpipes and combined systems are the way to go.  As
others have already mentioned, sprinkler floor controls on the
intermediate landing are awkward and often take up way too much volume
and floor space on intermediate landings, which are generally designed
only to the minimum required depth by archimitects.

Steve Leyton
Protection Design & Consulting
San Diego, CA


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Thursday, November 13, 2008 3:59 AM
To: [email protected]
Subject: RE: NFPA 14

The problem I hear is that hoses from an intermediate landing going 
up or down can create egress problems.



At 05:03 PM 11/12/2008, you wrote:
>None really, keep reading:  7.3.2.1 Hose connections shall be permitted
>to be located at the main floor landings ...
>
>In some jurisdictions, the connections are required to be on the
floors,
>other prefer the intermediates.  If you're in a state - such as
>California - that has a code amendment for high-rise buildings that
>requires the connections in the smoke-proof enclosures or stairs, you
>have no choice.
>
>The foregoing is my opinion only and does not necessarily represent the
>opinion or intent of the NFPA 14 Technical Committee on Standpipe and
>Hose Systems.
>
>Steve Leyton
>Protection Design & Consulting
>San Diego, CA
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of Autry,
>David
>Sent: Wednesday, November 12, 2008 1:44 PM
>To: [email protected]
>Subject: NFPA 14
>
>Speaking of Standpipes,
>NFPA 14 (2003, Edition) 7.3.2 (1)
>Class I standpipe systems shall be provided with 2 1/2" hose
connections
>at each intermediate landing between floor levels in every required
exit
>stairway.
>
>What are the ramifications of allowing the hose connections to be on
the
>floor landings?
>
>I realize the benefits to firefighters of the valve being between
>floors.
>
>The contractor submitted plans and I pointed out the code requires them
>to be at the intermediate landings. "Well that's where they're shown on
>the Mech. Plans." I ASSUME they were shown there by a PE of one
>discipline or another and were missed during the architectural review.
>
>It just seems to me to be a royal pain in the a** to install these
>valves at the intermediate landings.
>
>Any thoughts from the mighty Forum?
>
>
>David Autry
>Plans Examiner
>Nebraska State Fire Marshal's Office
>246 S. 14th Street
>Lincoln, NE 68508
>402-471-9659
>402-471-3118 fax
>www.sfm.ne.gov
>
>** Note new email address: [EMAIL PROTECTED]
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of
>[EMAIL PROTECTED]
>Sent: Wednesday, November 12, 2008 2:42 PM
>To: [email protected]
>Subject: Re: design and coordination roles and responsibilities.
>
>My favorite story in the ongoing battle between the professionals is
the
>difficulty Steve Leyton had with a registered PE who informed him that
>by the virtue of his lack of registration as a PE that he was
>"unqualified" to discuss the issues related to standpipe design, use,
>and compliance with NFPA-14.  The fact that Steve was a member of the
>NFPA-14 committee at the time escaped the notice of the individual, and
>in a delicious moment of irony Steve pointed to his name in the front
of
>the book.
>
>That was a day I'll long cherish.
>
>PARSLEY CONSULTING
>Ken Wagoner, SET
>760.745.6181 voice
>760.745.0537 fax
>[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
>www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
>
>
>
>Ron Greenman wrote:
> > Once I was called incompetent by the architect because in the field
> > there was one inch of clear space between the bottom of the beams in
a
> > parking garage and the minimum low clearance for the cars and I
> > couldn't fit a four inch pipe in the space (and I couldn't touch the
> > beams. He drew nine inches but the excavator screwed up, the garage
> > got poured and it was my problem somehow.
> >
> > On Wed, Nov 12, 2008 at 11:39 AM, Thom McMahon
><[EMAIL PROTECTED]> wrote:
> >
> >> Your RIGHT! Because the sprinkler contractor is now the only one
that
>does
> >> his layout in 3D he visualizes all of the problems the others call
>"Field
> >> Conditions".
> >> Architects get really pissed off when you point out that they and
>their
> >> consultants didn't co-ordinate space above the ceiling even with
>their own
> >> structural engineer. Yeah the ceiling to bottom of floor is 36",
and
>there
> >> are recessed lights in the ceiling with lenses that make them 8"
>deep. And
> >> yes you clearly show the 16x30 duct, and the cable tray and our
main
>is only
> >> 6", so what's your problem? COULD IT POSSABLY BE THAT W30 beam
we're
>all
> >> shown crossing?
> >>
> >> Since ancient times the builder of empires and Architects have had
>the same
> >> theory, KILL the messenger!!
> >>
> >> Thom McMahon, SET
> >> Firetech, Inc.
> >> 2560 Copper Ridge Dr
> >> P.O. Box 882136
> >> Steamboat Springs, CO 80488
> >> Tel:  970-879-7952
> >> Fax: 970-879-7926
> >>
> >>
> >> -----Original Message-----
> >> From: [EMAIL PROTECTED]
> >> [mailto:[EMAIL PROTECTED] On Behalf Of Todd
>Williams
> >> - FPDC
> >> Sent: Wednesday, November 12, 2008 10:59 AM
> >> To: [email protected]
> >> Subject: RE: design and coordination roles and responsibilities.
> >>
> >> One of the consistent problems we have up here is the electrician.
> >> They don't take part in the coordination process, they often don't
>even have
> >> CAD drawings and they just run everything where they want.
> >> And the GC's tend to let them get away with a lot of it. I find
that
>more
> >> problems with the architect's concepts surface in the sprinkler
>design that
> >> any of the other trades.
> >>
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> For Technical Assistance, send an email to:
>[EMAIL PROTECTED]
> >>
> >> To Unsubscribe, send an email
>to:[EMAIL PROTECTED]
> >> (Put the word unsubscribe in the subject field)
> >>
> >>
> >
> >
> >
> >
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
>[EMAIL PROTECTED]
>
>To Unsubscribe, send an email
>to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
>[EMAIL PROTECTED]
>
>To Unsubscribe, send an email
>to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)
>
>
>__________ Information from ESET NOD32 Antivirus, version of virus
>signature database 3607 (20081112) __________
>
>The message was checked by ESET NOD32 Antivirus.
>
>http://www.eset.com
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
[EMAIL PROTECTED]
>
>To Unsubscribe, send an email
to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to