The problem I hear is that hoses from an intermediate landing going
up or down can create egress problems.
At 05:03 PM 11/12/2008, you wrote:
None really, keep reading: 7.3.2.1 Hose connections shall be permitted
to be located at the main floor landings ...
In some jurisdictions, the connections are required to be on the floors,
other prefer the intermediates. If you're in a state - such as
California - that has a code amendment for high-rise buildings that
requires the connections in the smoke-proof enclosures or stairs, you
have no choice.
The foregoing is my opinion only and does not necessarily represent the
opinion or intent of the NFPA 14 Technical Committee on Standpipe and
Hose Systems.
Steve Leyton
Protection Design & Consulting
San Diego, CA
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Autry,
David
Sent: Wednesday, November 12, 2008 1:44 PM
To: [email protected]
Subject: NFPA 14
Speaking of Standpipes,
NFPA 14 (2003, Edition) 7.3.2 (1)
Class I standpipe systems shall be provided with 2 1/2" hose connections
at each intermediate landing between floor levels in every required exit
stairway.
What are the ramifications of allowing the hose connections to be on the
floor landings?
I realize the benefits to firefighters of the valve being between
floors.
The contractor submitted plans and I pointed out the code requires them
to be at the intermediate landings. "Well that's where they're shown on
the Mech. Plans." I ASSUME they were shown there by a PE of one
discipline or another and were missed during the architectural review.
It just seems to me to be a royal pain in the a** to install these
valves at the intermediate landings.
Any thoughts from the mighty Forum?
David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
** Note new email address: [EMAIL PROTECTED]
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, November 12, 2008 2:42 PM
To: [email protected]
Subject: Re: design and coordination roles and responsibilities.
My favorite story in the ongoing battle between the professionals is the
difficulty Steve Leyton had with a registered PE who informed him that
by the virtue of his lack of registration as a PE that he was
"unqualified" to discuss the issues related to standpipe design, use,
and compliance with NFPA-14. The fact that Steve was a member of the
NFPA-14 committee at the time escaped the notice of the individual, and
in a delicious moment of irony Steve pointed to his name in the front of
the book.
That was a day I'll long cherish.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
Ron Greenman wrote:
> Once I was called incompetent by the architect because in the field
> there was one inch of clear space between the bottom of the beams in a
> parking garage and the minimum low clearance for the cars and I
> couldn't fit a four inch pipe in the space (and I couldn't touch the
> beams. He drew nine inches but the excavator screwed up, the garage
> got poured and it was my problem somehow.
>
> On Wed, Nov 12, 2008 at 11:39 AM, Thom McMahon
<[EMAIL PROTECTED]> wrote:
>
>> Your RIGHT! Because the sprinkler contractor is now the only one that
does
>> his layout in 3D he visualizes all of the problems the others call
"Field
>> Conditions".
>> Architects get really pissed off when you point out that they and
their
>> consultants didn't co-ordinate space above the ceiling even with
their own
>> structural engineer. Yeah the ceiling to bottom of floor is 36", and
there
>> are recessed lights in the ceiling with lenses that make them 8"
deep. And
>> yes you clearly show the 16x30 duct, and the cable tray and our main
is only
>> 6", so what's your problem? COULD IT POSSABLY BE THAT W30 beam we're
all
>> shown crossing?
>>
>> Since ancient times the builder of empires and Architects have had
the same
>> theory, KILL the messenger!!
>>
>> Thom McMahon, SET
>> Firetech, Inc.
>> 2560 Copper Ridge Dr
>> P.O. Box 882136
>> Steamboat Springs, CO 80488
>> Tel: 970-879-7952
>> Fax: 970-879-7926
>>
>>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
>> - FPDC
>> Sent: Wednesday, November 12, 2008 10:59 AM
>> To: [email protected]
>> Subject: RE: design and coordination roles and responsibilities.
>>
>> One of the consistent problems we have up here is the electrician.
>> They don't take part in the coordination process, they often don't
even have
>> CAD drawings and they just run everything where they want.
>> And the GC's tend to let them get away with a lot of it. I find that
more
>> problems with the architect's concepts surface in the sprinkler
design that
>> any of the other trades.
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to:
[EMAIL PROTECTED]
>>
>> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>>
>
>
>
>
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
__________ Information from ESET NOD32 Antivirus, version of virus
signature database 3607 (20081112) __________
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080