Burton, 2006 IBC 903.4.2 "Where a fire alarm system is installed, actuation of the automatic sprinkler system shall actuate the building fire alarm system"
With that a) has a fire alarm system been installed ?, or is one required ? As Jim referenced (Section 907.2.7 in 2006 IBC) the occupant load criteria must be determined. Also is this strictly an M use or a mixed use ? Lastly assuming that a manual fire alarm system is required, did the owner take exception number 2 of 2006 IBC 907.2.7. and eliminate the manual stations in a fully sprinklered building ? So in a nutshell; 1) Fire Alarm installed, actuate the building fire alarm system. 2) Fire Alarm required, actuate the building fire alarm system if manual stations eliminated. 3) Check if any local amendments to adopted codes and standards in your area. Hope that helps John Drucker Fire Protection Subcode Official (AHJ) Red Bank, NJ -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Wednesday, November 19, 2008 4:44 PM To: [email protected] Subject: RE: Alarms Burton, I've gotten into this discussion before with clients. IFC-2006 907.2 and related 907.2.7 require the alarm system only where total occupancy exceeds 500 or 100 person above or below exit discharge. If you go above and beyond you have to install per NFPA 72 and then ADA also have to be followed. It is not mandatory per ADA to provide visual appliances unless they are being provided for hearing abled - every has to be treated the same. If necessary, I may be able to dig up the ADA section. James L.(Jim) Roberts, PE/SET Fluor Corporation 100 Fluor Daniel Drive - C104F Greenville, SC 29607 864.281.5149 864.281.4916(Fax) "Ford, Charles" <[EMAIL PROTECTED]> Sent by: [EMAIL PROTECTED] 11/19/2008 03:58 PM Please respond to sprinklerforum To <[email protected]> cc Subject RE: Alarms I'm embroiled in an argument ( technical discussion) regarding sprinkler alarms and I'd like to confirm or deny my understanding (and position) Given an existing fully sprinklered building of public occupancy say supermarket or restaurant (IBC Group M). Given an outside alarm is provided. 1. Is the interior of the building required to have evacuation alarms? 2. Must they be throughout re 72 and ADA? Controlling codes are IBC and IFC land I know we've discussed this earlier but somebody maybe me needs convincing C. Burton Ford Designer- NICET Certified: Fire Alarm, Special Hazards, Sprinkler Design &Sprinkler Inspections NFPA CFPS Cintas Fire Protection-D-47 Mamber This e-mail transmission contains information that is intended to be confidential and privileged. If you receive this e-mail and you are not a named addressee you are hereby notified that you are not authorized to read, print, retain, copy or disseminate this communication without the consent of the sender and that doing so is prohibited and may be unlawful. Please reply to the message immediately by informing the sender that the message was misdirected. After replying, please delete and otherwise erase it and any attachments from your computer system. Your assistance in correcting this error is appreciated. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) ------------------------------------------------------------ The information transmitted is intended only for the person or entity to which it is addressed and may contain proprietary, business-confidential and/or privileged material. If you are not the intended recipient of this message you are hereby notified that any use, review, retransmission, dissemination, distribution, reproduction or any action taken in reliance upon this message is prohibited. If you received this in error, please contact the sender and delete the material from any computer. Any views expressed in this message are those of the individual sender and may not necessarily reflect the views of the company. ------------------------------------------------------------ _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)