Rod,

You're absolutely right, Thanks


Eladio Alvarado
Fire Protection Systems Inc.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Rod DiBona
Sent: Wednesday, November 19, 2008 10:08 PM
To: [email protected]
Subject: RE: Hydraulic Calculations

Eladio,

I think what Todd is referring to is not neccesarily the literal "remote
area" but the hydraulically most demanding remote area which is what needs
to be calculated. In other words in your situation you may have just created
a situation where these heads are more demanding than the heads on the next
floor up and in fact it seems that all things equal this is a probability.
No question here that a calculation should be done. Good Luck.

Rod DiBona
Rapid Fire

________________________________

From: [EMAIL PROTECTED] on behalf of Eladio N.
Alvarado
Sent: Wed 11/19/2008 1:24 PM
To: [email protected]
Subject: RE: Hydraulic Calculations



Todd:

Thanks for your response, and I agree with you on the additional water
required due to the minimum discharge criteria, but I think my confusion
comes from the assumption that the same square feet area is protected by 2x
the number of sprinklers and since sometimes small areas such as closets are
not included in the calculations, this duplication on the pattern would not
necessitate the re-calc. However I'm following your advice and will
recalculate. By the way the remote area is in fact at the third floor level,
this condition arose at the basement level. Thanks again for your help.

Eladio Alvarado
Fire Protection Systems Inc.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Todd Williams
Sent: Wednesday, November 19, 2008 6:26 AM
To: [email protected]
Subject: Re: Hydraulic Calculations

Eladio,

This should be calculated. For one thing, the new arrangement may now
be the most hydraulically remote. Assuming that the protection
requirements will not change, with 12x14 spacing and 0.1 density, you
will be flowing 16.8 gpm per sprinkler. However, with the 6x14
spacing, the minimum 7 psi requirement will kick in and you will need
to flow 14.8 gpm per sprinkler. Before you had X sprinklers
calculated flowing 16.8 gpm each (min), now you will have 2X
sprinklers flowing at 14.8 gpm each. A whole lot more water. Do the math.


At 04:27 AM 11/19/2008, you wrote:
>Forum:
>   I would appreciate insight into the following questions. If I have a
Light
>Hazard room where the original design set sprinklers in a pattern of 12 x
14
>ft, now they have introduced book racks taller than the original proposed
>thus requiring that this pattern and already installed pipe be altered to
>accommodate more sprinklers within the shelving units, sprinklers will now
>be located 6 x 14 ft pattern. The basic change will be achieved by
>installing 2 sprinklers from each of the originally installed outlets. The
>AHJ (A/E) is now requiring hydraulic calculations to justify the additional
>sprinklers. This area is not the most remote area of the project, so the
>question is; Aside from the fact that the changes do not affect the
>hydraulically calculated area, we argue that hydraulic calculations are
>based on area or room coverage and not in number of sprinklers, so since we
>have proved that we meet the required density with sprinklers that cover
168
>Sq. Ft., it is not necessary that we revise these calculations to show
>density on sprinklers now covering 84 Sq. Ft. instead.
>Am I right?
>
>Eladio Alvarado
>Fire Protection Systems Inc.
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [EMAIL PROTECTED]
>
>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to