I've been trying to find my way through section 17.3 (2007 ed) and I've
been finding some conflicting paragraphs and some paragraphs that seem
to be under the wrong header. For instance, table 17.3.1.1 gives
area/density requirements of 0.30 or 0.45 for ceiling sprinklers (for
single row, double row and multi-row racks) depending on the distance
from the top of storage to the top level of in-rack sprinklers. Reading
further through the chapter at paragraph 17.3.4.1.4 (which is actually
under the heading of in-rack sprinkler location) it says that for single
and double row racks the ceiling density shall be 0.45 gpm/sq ft. Where
did the 0.30 density option go?


Thanks,
Ed Tambini
Aero Automatic Sprinkler Co.
Phoenix, AZ