The Australian sprinkler code prohibits this. There are very good
reasons for this. If you use steel pipe it will corrode and leak. If you
use copper or plastic pipe it will be damaged during construction (bent
or squashed during pouring of the concrete) and may leak or not allow
the required amount of water to pass through. Any changes to sprinkler
locations required due to later architectural changes are impossible to
achieve. In the past when the code did not prohibit this some buildings
were built with pipe cast into the slab. There were some disasters and 5
to 10 years later the buildings had to be retro fitted with pipe below
the slabs due to leaks (very difficult jobs). I would not recommend
casting sprinkler systems into slabs.

Regards

Frank Hull
Technical Manager
Wormald

Tyco Fire & Security Australia/New Zealand

Unit 1 2-8 South Street
Rydalmere, NSW
Australia 2116

Phone: +61 2 9638 8511
Fax: +61 2 9638 8599
Mobile: 0411 022 837

ATTENTION RECIPIENT: This email and any attachments are confidential and
may be legally privileged. Confidentiality and/or privilege is not
waived or lost by mistaken delivery. If you are not the intended
recipient of this email, please notify us immediately and delete it from
your system. Unauthorised use of this email is prohibited. Any personal
information in this email must be treated in accordance with applicable
privacy laws.

P Be earthsmart.  Please consider the environment before printing this
e-mail. 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of R
Richardson
Sent: Wednesday, 17 December 2008 1:45 AM
To: [email protected]
Subject: Pipe Installed in concrete

We have a proposal to install sprinkler pipe within a poured concrete
floor/ceiling.   Has anyone dealt with this or done it themselves?
Good, bad or ugly.

Thanks,

Rich Richardson
Seattle Fire Department

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to