There seems to be a common misconception concerning the official status of FM 
guidelines.  NFPA is an adopted Standard which in most if not all jurisdictions 
is part of the legally adopted building code.  When adopted as part of the code 
it is part of the law of that state or local jurisdiction.  Any code official 
who's worth anything will tell you that his duty is to uphold the laws of his 
state when it comes to building and construction.  (Ok, in  a perfect world, go 
with me on this)

FM Data sheets are tremendous tools and are used by many to determine 
protection criteria for those special systems that the Codes do not always 
address. BUT, the FM data sheets are not part of the building code.  They can 
be used as an addition or supplement to the basic NFPA Standard but they are 
the guidelines from an insurance entity.  The FM recommendations are typically 
negotiable between the insurer and the owner, Code requirements are usually 
non-negotiable (there are variances for certain things).  I don't know of any 
building official that will tell you to use FM in place of NFPA. An insurance 
underwriter would be the one to tell you if they have recommendations beyond 
NFPA which they would require/request.

In no way am I discrediting the FM data, it is priceless but it is not the same 
as NFPA from a legal standpoint.

Anyway, back to the main topic.................

Check out the commentary in FMDS 7-11. It addresses the air flow issue.  




Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jay Jay Blocker
Sent: Tuesday, February 03, 2009 11:21 PM
To: [email protected]
Subject: Re: Sprinkler protection below conveyors in pits

Well yes and noon the interlock issue but thats not really the issue at hand.  
In order to find out if FM or NFPA is going to be the standard I would consult 
the AHJ to get the perspective of the individual that says yes or no.  I have 
yet to find an AHJ that says FM will be used to substitute NFPA simply due to 
liability.  If not listed for there intended use just simply ask the AHJ to 
sign off on it then the situation is resolved.  If they will not sign off on 
that look at the deluge system.  Mines are a creature all there own and rarely 
found to resemble the next.  The main reason for this is do primarily to the 
length of the conveyor and type of material it transports.  As far as the 
interlock goes we all know how the fire tetrahedron works.  The stopping of the 
belt is not so the fire wont outrun the sprinklers it is to limit air 
flow which is fueling the fire.  The fire can only out run the sprinklers if 
the proper fuel base is  there, so we limit the extra ingredients.  

Keep us informed.
 
Jeremy S. Blocker
 
Let us not look back in anger, nor forward in fear, but around in awareness. 
--James Thurber 




________________________________
From: Rod DiBona <[email protected]>
To: [email protected]
Sent: Tuesday, February 3, 2009 8:44:28 AM
Subject: RE: Sprinkler protection below conveyors in pits

Well I have a different opinion on this Craig. Most of the time the ONLY reason 
that many of these industrial sites are getting any fire protection is because 
the insurer is asking for it. We have about seventy mining sites in our working 
area and the majority of them have very little or no protection at all. When 
the insurer is the one coming in and ASKING the owner to sprinkler a certain 
hazard he is also the one telling them how it will be done to receive the 
proper premium credit. I have had several instances in the last year dealing 
with this exact issue. On one of the projects where the sprinkler alone was $10 
million I adamantly asked that we cover the top and bottom belt on thousands of 
feet of new belts that were being built. I showed NFPA 15 and even had a 
proposal that showed that it was even more important with Powder River Coal 
because of its higher propensity to spontaneous combustion. This was a piece 
done by the powder river coal group. At the end of the day the engineers said 
no because FM was not requiring it. Their data sheets only require the top 
belt. It is one of the few times that I have seen where the FM data sheets were 
clearly less restrictive than NFPA. 

Secondly most of these systems that I have seen are not deluge. This is due to 
hydraulic restrictions of large deluge systems and physical restrictions due to 
parallel runs of bulk needed for several deluge systems. Most of these systems 
are preaction that I have seen. As you referenced there is an interlock that 
shuts down the conveyor upon activation isn't that so that the fire doesn't 
"out run the sprinklers."

Rod DiBona
Rapid Fire

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, February 03, 2009 6:56 AM
To: [email protected]
Subject: RE: Sprinkler protection below conveyors in pits

First, Unless FM's guidelines exceed NFPA I wouldn't be replacing the NFPA 
standard with the FM guidelines since NFPA is usually referenced in the 
building codes and FM's Data Sheets are not.  So if NFPA says do top and bottom 
and FM says only do bottom I'd be doing top and bottom.

Second, Conveyor system protection is found in more detail in NFPA 15 (7.2.3, 
2007) since these are almost always deluge type systems.
Definitely would not want to use closed heads in this application as the fire 
could out run the sprinklers or the sprinklers may not respond at all due to 
the belt movement.

A typical installation would consist of open spray nozzles usually with a broad 
angle spray pattern with linear heat detection or other heat detection method 
to set the system off. Manual activation is also a common accessory to the 
system.

Also it wasn't stated what was being conveyed.  There are other NFPA Standards 
for various industries or hazards which provide additional information on 
protection of conveyors in specific applications. 

With open nozzles such as Tyco's Protectospray or Reliable's Model A or 
Viking's Model E or other similar, you can select the discharge angle up to 180 
degrees,  the nozzle can be placed with a few feet of the object you are 
protecting with no loss of integrity of the spray pattern.  This is something 
you can not accomplish with a typical SSU or SSP.  They are not made for this 
type of application.  You must determine the appropriate spray angle as you 
determine the distance between the nozzle and the belt (axial distance).  As 
you get closer to the belt naturally the spray pattern area will get smaller.  
Also understand that you have various K-factors to choose from.  Choose the 
correct K-factor nozzle to deliver the needed amount of water to the hazard.  
You do not need to use just 5.6K's everywhere.  If this is an enclosed conveyor 
make sure the structural people as well as the conveyor mfgr. know about how 
much water you will be introducing into the enclosure so they can provide 
adequate drainage capabilities.  

Remember if you go below a certain size orifice (I think it's 3/8") you will 
have to provide a strainer on the system.  

Don't forget to discuss system interlocks for belt movement interruption with 
the conveyor vendor and owner.  

Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rod DiBona
Sent: Monday, February 02, 2009 6:49 PM
To: [email protected]
Subject: RE: Sprinkler protection below conveyors in pits

We have used nozzles that can be selected with various spray patterns in this 
situation. Also something that we have recently discovered is that if this is 
an FM insured property they normally do not require the return belt to be 
covered even though NFPA is clear that it should be.
If not FM then we find a solution that most closely complies the standard and 
listing and present that to the powers to be. It is not always possible to 
comply 100%.

Rod DiBona
Rapid Fire

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ryan Hinson
Sent: Monday, February 02, 2009 3:56 PM
To: [email protected]
Subject: Sprinkler protection below conveyors in pits

Where would I go to properly protect below conveyors in pits that there is less 
then 4' of clear space below the return loop of the conveyor and the conveyer 
belt is 60" wide with SSU's?  NFPA 13(2002) section 8.6.5 does not address this 
situation in my opinion.  What is the space depth at which sprinklers are no 
longer able to develop the water pattern necessary to be practicable?



Thank you,



Ryan L. Hinson, EIT, CET, Nicet III

FP Design Manager

Fire Construction Design Services, LLC #C124

A Division of Fire Construction Services, Inc.

6950-43rd Avenue SE

St. Cloud, MN 56304

Direct:  320-250-5404 

Fax: 320-358-3495

email:  <mailto:[email protected]>
[email protected]



CONFIDENTIALITY NOTICE: The information contained in this message, including 
any files transmitted within, is confidential, may be legally privileged, and 
is intended only for the use of the individual(s) named above. The use of any 
confidential or personal information may be restricted by state and federal 
privacy laws.  If this message was received in error, please notify the sender 
and then delete this message.



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to