I have been following this thread for several days now and while in general
terms I believe that Craig is correct, in the specific instance Rod is
describing I believe he is also correct.

3.2.2* Authority Having Jurisdiction (AHJ). An organization,
office, or individual responsible for enforcing the requirements
of a code or standard, or for approving equipment,
materials, an installation, or a procedure.

If the building Code and by association the Fire Code and adopted standards,
did not require protection for the conveyor belts in the first place, and
the installation is only to satisfy the insurance underwriter, that has
their own standards, they are the AHJ.

Yes we could go on that same old song, "If you do it, it has to be to Code
or Standard" and I would argue that this is one instance of the only one
that cares is the underwriter, and he is the one covering the risk. It's not
a perfect world, and in theory Craig is correct, and in practical terms rod
is correct. In financial terms only a fire will tell.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, February 04, 2009 6:41 AM
To: [email protected]
Subject: RE: Sprinkler protection below conveyors in pits

There seems to be a common misconception concerning the official status of
FM guidelines.  NFPA is an adopted Standard which in most if not all
jurisdictions is part of the legally adopted building code.  When adopted as
part of the code it is part of the law of that state or local jurisdiction.
Any code official who's worth anything will tell you that his duty is to
uphold the laws of his state when it comes to building and construction.
(Ok, in  a perfect world, go with me on this)

FM Data sheets are tremendous tools and are used by many to determine
protection criteria for those special systems that the Codes do not always
address. BUT, the FM data sheets are not part of the building code.  They
can be used as an addition or supplement to the basic NFPA Standard but they
are the guidelines from an insurance entity.  The FM recommendations are
typically negotiable between the insurer and the owner, Code requirements
are usually non-negotiable (there are variances for certain things).  I
don't know of any building official that will tell you to use FM in place of
NFPA. An insurance underwriter would be the one to tell you if they have
recommendations beyond NFPA which they would require/request.

In no way am I discrediting the FM data, it is priceless but it is not the
same as NFPA from a legal standpoint.

Anyway, back to the main topic.................

Check out the commentary in FMDS 7-11. It addresses the air flow issue.  




Craig L. Prahl, CET   