braces and their associated zone of influence are assigned to a
straight run of pipe. Naturally this is not stated in the standard
but if you can follow a little ciphering by Jethro, you'll arrive at
the right answer. If you aren't a graduate of an Ivy league school,
like Jethro (or Dubya), looking at A.9.3.5.3.1 should help.
Roland
On Feb 4, 2009, at 11:58 AM, Bob Knight wrote:
I have a hexagonical building that has branch lines gridded around the
hexagon. When considering my zone-of-influence for the sway bracing
do I
need to consider the complete force of the branch line, which is a
hexagonical circle as it were, or do I just consider the branch line
up to
the first change of direction in the hexagon?
I don't see how the horizontal force from across the building is
going to
impact the main when the force would be passing through 3 changes of
direction with each change of direction having a swing joint.
So, I guess that my question is, when I sway brace the main do I
consider
the load of the branch line up to the fist change of direction, or
do I
consider the entire load around the building? There is no secondary
grid
main, since the primary main acts as both.
Bob Knight, CET
(208) 318-3057
[email protected]
www.firebyknight.com
No virus found in this outgoing message.
Checked by AVG - www.avg.com
Version: 8.0.233 / Virus Database: 270.10.18/1935 - Release Date:
02/04/09
16:35:00
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)