Installing intermediate temperature sprinklers seems like the most
sensible approach, but you could not reinstall them elsewhere because
they are now "used".

Paul Pinigis, P.E.
Life Safety Department Head



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thomas
Watt
Sent: Friday, February 06, 2009 8:21 AM
To: [email protected]
Subject: * Possible Spam *Bedbug Treatment

Hello group,

Several months ago I was sent to remove the (12)sprinklers from a hotel
room so that it could be heat treated for a bedbug infestation. This
process involves heating the room to over 130 degrees. My instructions
were to remove the sprinklers and replace with nipple/caps until the
next day when the sprinklers could be replaced.

I know in many cases the heating equipment is truck mounted and the
heating ducts are stretched into the unit to be treated. In this case,
the heater/blowers were all portable units. In retrospect, with all of
these appliances in this unprotected space in an occupied wing of this
hotel, this was a catastrophe waiting to happen. 

1) Could I have replaced the 155* heads with intermediate temp heads?
2) Could I reuse these heads for the next bedbug job?

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to