This falls under 8.4.7 which is the large drop sprinklers section so I believe it can only be applied to this section. So what we are saying is that friction loss through the fittings are independent of the c-factor of the pipe.
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Thom McMahon Sent: Tuesday, February 10, 2009 12:30 PM To: [email protected] Subject: RE: galv fittings and dry system 8.4.7.2.2 not the fittings. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of George Church Sent: Tuesday, February 10, 2009 11:25 AM To: [email protected] Subject: RE: galv fittings and dry system I never did -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Dewayne Martinez Sent: Tuesday, February 10, 2009 1:19 PM To: [email protected] Subject: galv fittings and dry system If you use galv pipe for a dry system do you also have to use galv fittings in order to use C=120 in your hydraulic calculations? Thanks, Dewayne _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)