Thanks for all the help.  I understand the error of my ways now.  
Dewayne 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Joe
Hankins
Sent: Tuesday, February 10, 2009 1:52 PM
To: [email protected]
Subject: Re: galv fittings and dry system

The physical pipe length of a fitting is small, and that is all that
would be affected by galvanizing or not. . The "equivalent length" 
reflects the loss due to change in direction, etc.  The equivalent
length approach is an extremely rough approximation of loss in fittings
developed in the day when actually calculating the losses would have
been extremely time consuming.  For those who routinely report pressures
to the tenth (or hundredth!) of a pound, the accuracy of the equivalent
length method is on the order of  pounds, not tenths.

Dewayne Martinez wrote:
> This falls under 8.4.7 which is the large drop sprinklers section so I

> believe it can only be applied to this section.
> So what we are saying is that friction loss through the fittings are
> independent of the c-factor of the pipe.   
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Thom 
> McMahon
> Sent: Tuesday, February 10, 2009 12:30 PM
> To: [email protected]
> Subject: RE: galv fittings and dry system
>
> 8.4.7.2.2 not the fittings.
>
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel:  970-879-7952
> Fax: 970-879-7926
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of George 
> Church
> Sent: Tuesday, February 10, 2009 11:25 AM
> To: [email protected]
> Subject: RE: galv fittings and dry system
>
> I never did
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Dewayne

> Martinez
> Sent: Tuesday, February 10, 2009 1:19 PM
> To: [email protected]
> Subject: galv fittings and dry system
>
> If you use galv pipe for a dry system do you also have to use galv 
> fittings in order to use C=120 in your hydraulic calculations?
> Thanks,
> Dewayne
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: 
> [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>   

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to