NFPA 13R has a very reasonable rule as stated in the 2007 edition below. Is there any rule that would address the same situation that can be found in NFPA 13.
If not, can anyone tell me if there was a proposal submitted to address this issue. It would go far in address blind spots in bathrooms and closets etc that are within an NFPA 13 installation. Thanks Pete Larrimer VA 6.8.1.5.3* Obstructions to Residential Sprinklers. 6.8.1.5.3.1 Closets. In all closets, including those closets housing mechanical equipment, that are not larger than 400 ft3 (11.33 m3) in size, a single sprinkler at the highest ceiling space in the closet shall be sufficient without regard to obstructions. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)