All of our testing has shown no problem caused by combined steel and
CPVC systems except for Allied ABF II.  I expect more coated steel pipe
to be added to compatibility list except Allied ABF II


Top Myers
RelMark Group
961 Pottstown Pike
Chester Springs, PA 19425
Office 610-321-2415   Cell 610-952-0965
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Friday, February 27, 2009 11:46 AM
To: [email protected]
Subject: CPVC and steel pipe

On a related note, Blazemaster has added Wheatland pipe with anti- 
microbial coating to its' Chemical Compatibility list.

Roland

On Feb 27, 2009, at 7:15 AM, George Church wrote:

> Is the possibility of MIC greater than the likelihood of ESF from MIC
> coatings? This would aid us in deciding, on systems comprised of  
> combo steel
> and CPVC, if we want to use uncoated pipe (more susceptible to MIC)  
> or risk
> Environmental Stress Fractures?