Forest,

Fat, short systems with fire pumps like you'd find in tire warehouse.
Sometimes jockeys can't keep up with expansion and contraction between
day and night. Took a long time to figure this out since I got the
call after the trip rather than before. If you want to get real fancy
you can use an automatic air release from a fire pump. I doubt though
that that would be a listed application. George's reasons also.

On Sun, Mar 1, 2009 at 7:43 AM, Forest Wilson <[email protected]> wrote:
> What advantage is there to venting the air? Other than response time?
> Sent from my Verizon Wireless BlackBerry
>
> -----Original Message-----
> From: "George Church" <[email protected]>
>
> Date: Sun, 1 Mar 2009 10:12:12
> To: <[email protected]>
> Subject: RE: statistics
>
>
> Nothing fancy, a 1" ball valve; or an ITC-type set up if you want to get
> fancy and run it out, we don't always.
>
> Potter has an auto air release you could also use.
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ergo
> Sent: Sunday, March 01, 2009 10:02 AM
> To: [email protected]
> Subject: Re: statistics
>
> George,
>
> You have a way to bleed the air off of the system at the high point? This
> sounds like a good idea. Cold you explain some more on how to make this
> happen?
>
> Thanks,
>
>
> Ergo
>
>
>
> On Fri, Feb 27, 2009 at 8:38 AM, George Church <[email protected]> wrote:
>
>> Venus and Mars. I raise hypothetical questions, you hunter-gatherers
> answer
>> the question instead of pursuing the issue of statistics :) and how to
> find
>> them. Quite a change from the suggester of a group hug:)
>>
>> I agree on the BFP, MIC, and although we often have the ITC on a riser
>> manifold, we generally have a way to bleed the air off the high point to
>> avoid false signals.
>>
>> Good point on calculating the Expected Value, taking the frequency a step
>> further and including impact.
>>
>> glc
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Chris
>> Cahill
>> Sent: Friday, February 27, 2009 11:02 AM
>> To: [email protected]
>>  Subject: RE: statistics
>>
>> But if you are doing a risk analysis you are forgetting the outcome side.
>> For example, failure of a BFP to protect the public in theory could be
>> catastrophic to many if not all on the water supply.  Failure of a BFP in
> a
>> fire should only affect one building. On the theoretical side some may die
>> from the fire and/or billions of $ lost but it ain't getting a whole city
>> sick or contaminating an aquifer used by 10's of millions.  So the rates
>> alone are irrelevant.  You need to take risk and multiply it by loss then
>> you have the answer on which way to go.  Don't get me wrong BFP's are a
>> bunch of hooey.
>>
>> 1st question - about 0 for both, BFP's are a waste of money in the first
>> place.
>>
>> 2nd - MIC is an issue we need to or will be dealing with more often.
>> Remember ESF only seems at this point to be an Allied problem. I vote
> treat
>> the MIC.
>>
>> 3rd - off the end gets some/most air out reducing false alarms and
>> eliminating some air/water interface rusting.  MIC coatings help with the
>> added oxygen in the water.  I vote end.
>>
>> Chris Cahill, P.E.
>> Fire Protection Engineer
>> Sentry Fire Protection, Inc.
>>
>> 763-658-4483
>> 763-658-4921 fax
>>
>> Email: [email protected]
>>
>> Mail: P.O. Box 69
>>        Waverly, MN 55390
>>
>> Location: 4439 Hwy 12 SW
>>              Waverly, MN 55390
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of George
>> Church
>> Sent: Friday, February 27, 2009 9:15 AM
>> To: [email protected]
>> Subject: statistics
>>
>> Just as we recently discussed that we don't know how many heads a year are
>> installed, or how many have been installed in the past 100+ years, when
>> discussing unexpected activations, statistics of some order of magnitude
>> would be helpful in numerous other things.
>>
>> Which occurs more frequently, failure of a backflow to protect the public
>> supply, or failure of a backflow to allow full forward flow of water to a
>> sprinkler system when needed?
>>
>> Is the possibility of MIC greater than the likelihood of ESF from MIC
>> coatings? This would aid us in deciding, on systems comprised of combo
>> steel
>> and CPVC, if we want to use uncoated pipe (more susceptible to MIC) or
> risk
>> Environmental Stress Fractures?
>>
>> Is it better to run the ITC off the riser and limit the new oxygen into
> the
>> system, or run it off the tail end and check for blockage?
>>
>> There are countless other items we have no data upon which to base our
>> decisions. Our best guesses may be completely wrong- guess our batting
>> average would be no better than 50-50, and likely the answer may be based
>> on
>> something more important but not considered.
>>
>> glc
>>
>> -----Original Message-----
>> From: George Church [mailto:[email protected]]
>> Sent: Friday, February 27, 2009 10:07 AM
>> To: '[email protected]'
>> Subject: RE: Fire marshall
>>
>> Just as a plumber would assume testing a sprinkler backflow is limited to
>> the backflow portion of the test, not aware of the forward flush we're
> more
>> concerned about.
>>
>> glc
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
> to:[email protected]<to%3asprinklerforum-requ...@fire
> sprinkler.org>
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
> to:[email protected]<to%3asprinklerforum-requ...@fire
> sprinkler.org>
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
> to:[email protected]<to%3asprinklerforum-requ...@fire
> sprinkler.org>
>> (Put the word unsubscribe in the subject field)
>>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....