Nothing fancy, a 1" ball valve; or an ITC-type set up if you want to get
fancy and run it out, we don't always.

Potter has an auto air release you could also use.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ergo
Sent: Sunday, March 01, 2009 10:02 AM
To: [email protected]
Subject: Re: statistics

George,

You have a way to bleed the air off of the system at the high point? This
sounds like a good idea. Cold you explain some more on how to make this
happen?

Thanks,


Ergo



On Fri, Feb 27, 2009 at 8:38 AM, George Church <[email protected]> wrote:

> Venus and Mars. I raise hypothetical questions, you hunter-gatherers
answer
> the question instead of pursuing the issue of statistics :) and how to
find
> them. Quite a change from the suggester of a group hug:)
>
> I agree on the BFP, MIC, and although we often have the ITC on a riser
> manifold, we generally have a way to bleed the air off the high point to
> avoid false signals.
>
> Good point on calculating the Expected Value, taking the frequency a step
> further and including impact.
>
> glc
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Chris
> Cahill
> Sent: Friday, February 27, 2009 11:02 AM
> To: [email protected]
>  Subject: RE: statistics
>
> But if you are doing a risk analysis you are forgetting the outcome side.
> For example, failure of a BFP to protect the public in theory could be
> catastrophic to many if not all on the water supply.  Failure of a BFP in
a
> fire should only affect one building. On the theoretical side some may die
> from the fire and/or billions of $ lost but it ain't getting a whole city
> sick or contaminating an aquifer used by 10's of millions.  So the rates
> alone are irrelevant.  You need to take risk and multiply it by loss then
> you have the answer on which way to go.  Don't get me wrong BFP's are a
> bunch of hooey.
>
> 1st question - about 0 for both, BFP's are a waste of money in the first
> place.
>
> 2nd - MIC is an issue we need to or will be dealing with more often.
> Remember ESF only seems at this point to be an Allied problem. I vote
treat
> the MIC.
>
> 3rd - off the end gets some/most air out reducing false alarms and
> eliminating some air/water interface rusting.  MIC coatings help with the
> added oxygen in the water.  I vote end.
>
> Chris Cahill, P.E.
> Fire Protection Engineer
> Sentry Fire Protection, Inc.
>
> 763-658-4483
> 763-658-4921 fax
>
> Email: [email protected]
>
> Mail: P.O. Box 69
>        Waverly, MN 55390
>
> Location: 4439 Hwy 12 SW
>              Waverly, MN 55390
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of George
> Church
> Sent: Friday, February 27, 2009 9:15 AM
> To: [email protected]
> Subject: statistics
>
> Just as we recently discussed that we don't know how many heads a year are
> installed, or how many have been installed in the past 100+ years, when
> discussing unexpected activations, statistics of some order of magnitude
> would be helpful in numerous other things.
>
> Which occurs more frequently, failure of a backflow to protect the public
> supply, or failure of a backflow to allow full forward flow of water to a
> sprinkler system when needed?
>
> Is the possibility of MIC greater than the likelihood of ESF from MIC
> coatings? This would aid us in deciding, on systems comprised of combo
> steel
> and CPVC, if we want to use uncoated pipe (more susceptible to MIC) or
risk
> Environmental Stress Fractures?
>
> Is it better to run the ITC off the riser and limit the new oxygen into
the
> system, or run it off the tail end and check for blockage?
>
> There are countless other items we have no data upon which to base our
> decisions. Our best guesses may be completely wrong- guess our batting
> average would be no better than 50-50, and likely the answer may be based
> on
> something more important but not considered.
>
> glc
>
> -----Original Message-----
> From: George Church [mailto:[email protected]]
> Sent: Friday, February 27, 2009 10:07 AM
> To: '[email protected]'
> Subject: RE: Fire marshall
>
> Just as a plumber would assume testing a sprinkler backflow is limited to
> the backflow portion of the test, not aware of the forward flush we're
more
> concerned about.
>
> glc
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]<to%3asprinklerforum-requ...@fire
sprinkler.org>
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]<to%3asprinklerforum-requ...@fire
sprinkler.org>
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]<to%3asprinklerforum-requ...@fire
sprinkler.org>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to