Anyone had this issue with areas above suspended ceilings? 

 

I have an "attic" composed of non-combustible and limited combustible
material. It is steel with noncombustible insulation and an insulation
barrier with a flame spread index of 10 on the exposed side (15 on the
insulation side) above suspended ceiling tiles with a class A fire rating
(flame spread of 25 or under).

 

The AHJ is telling me I need sprinklers in this area because the insulation
barrier is not ridged per NFPA 13/2007 8.15.1.2.10. I thought if it
conformed to 3.3.11 limited-combustible material definition it would not
need to be sprinklered per 8.15.1.2.1. 

 

Thanks,

 

Chris Russell