Hope this will help


IMC, Section 602.2.1



Materials exposed within plenums. Except as required by Sections 602.2.1.1 
through 602.2.1.5, materials within plenums shall be noncombustible or shall 
have a flame spread index of not more than 25 and a smoke-developed index of 
not more than 50 when tested in accordance with ASTM E 84.



Exceptions:



1. Rigid and flexible ducts and connectors shall conform to Section 603.



2. Duct coverings, linings, tape and connectors shall conform to Sections 603 
and 604.



3. This section shall not apply to materials exposed within plenums in one- and 
two-family dwellings.



4. This section shall not apply to smoke detectors.



5. Combustible materials enclosed in no-combustible raceways or enclosures, 
approved gypsum board assemblies or enclosed in materials listed and labeled 
for such application.





Jaber Al-Haji

S.Aramco

Loss Prevention Dept

[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Chris Russel
Sent: Monday, March 02, 2009 9:14 PM
To: [email protected]
Subject: Limited combustible material above suspended ceilings



Hello,







Anyone had this issue with areas above suspended ceilings?







I have an "attic" composed of non-combustible and limited combustible

material. It is steel with noncombustible insulation and an insulation

barrier with a flame spread index of 10 on the exposed side (15 on the

insulation side) above suspended ceiling tiles with a class A fire rating

(flame spread of 25 or under).







The AHJ is telling me I need sprinklers in this area because the insulation

barrier is not ridged per NFPA 13/2007 8.15.1.2.10. I thought if it

conformed to 3.3.11 limited-combustible material definition it would not

need to be sprinklered per 8.15.1.2.1.







Thanks,







Chris Russell



t. 360.734.4940

f. 360.647.9540



securitysolutionsnw.com







_______________________________________________

Sprinklerforum mailing list

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]



To Unsubscribe, send an email to:[email protected]

(Put the word unsubscribe in the subject field)

________________________________
The contents of this email, including all related responses, files and 
attachments transmitted with it (collectively referred to as "this Email"), are 
intended solely for the use of the individual/entity to whom/which they are 
addressed, and may contain confidential and/or legally privileged information. 
This Email may not be disclosed or forwarded to anyone else without 
authorization from the originator of this Email. If you have received this 
Email in error, please notify the sender immediately and delete all copies from 
your system. Please note that the views or opinions presented in this Email are 
those of the author and may not necessarily represent those of Saudi Aramco. 
The recipient should check this Email and any attachments for the presence of 
any viruses. Saudi Aramco accepts no liability for any damage caused by any 
virus/error transmitted by this Email.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to