Anna,

Are they shelves or racks?


At 09:39 AM 3/11/2009, you wrote:
>Gentlemen, Would you please help me? I have the 
>basement in student’s dorm serving as a storage 
>room approximate 2000  sqft. Around all storage 
>room, along walls, there are storage racks with 
>the solid wood  shelves (storage racks are about 
>680 sqft). The storage contains beddings: 
>sheets,  pillows and comforters in the small 
>plastic bags. Room is 9 ft height; first level 
>of rack is 2 ft above floor and second level 5 
>ft above  floor. Commodities are stored to the 
>ceiling of the room. Please correct me if my 
>approach is not correct: 1. Storage classified 
>as miscellaneous storage 2. Commodities 
>classification: Class IV 3. Storage to be lower 
>min. 18 inch from the sprinklers. 3. Design 
>criteria for ceiling sprinklers based on 12.1.10 
>(NFPA 13 2002): 1500sqft/0.20  gpm/sqft  4. 
>Since we have solid shelving do we need have in 
>rack sprinklers and need to apply  section 
>12.3.1.9.2 “Where solid shelving in single-, 
>double-, and multiple-row racks  exceeds 64 sqft 
>in are or where the level of storage exceed 6 
>ft, sprinklers shall be  installed at the 
>ceiling and below each level of shelving”? It 
>is not really clear to me that this requirement 
>applies to miscellaneous storage also. I would 
>really appreciate you help. Thank you, Anna 
>Reich 
>_______________________________________________ 
>Sprinklerforum mailing list 
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
>For Technical Assistance, send an email to: 
>[email protected] To Unsubscribe, 
>send an email 
>to:[email protected] (Put 
>the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________