They are racks since they are 36" and 48" wide.

Racks are built with steel support attached to wall with solid wood on the top 
of shelves.



Thanks,


---- Todd Williams <[email protected]> wrote: 
> Anna,
> 
> Are they shelves or racks?
> 
> 
> At 09:39 AM 3/11/2009, you wrote:
> >Gentlemen, Would you please help me? I have the 
> >basement in student’s dorm serving as a storage 
> >room approximate 2000  sqft. Around all storage 
> >room, along walls, there are storage racks with 
> >the solid wood  shelves (storage racks are about 
> >680 sqft). The storage contains beddings: 
> >sheets,  pillows and comforters in the small 
> >plastic bags. Room is 9 ft height; first level 
> >of rack is 2 ft above floor and second level 5 
> >ft above  floor. Commodities are stored to the 
> >ceiling of the room. Please correct me if my 
> >approach is not correct: 1. Storage classified 
> >as miscellaneous storage 2. Commodities 
> >classification: Class IV 3. Storage to be lower 
> >min. 18 inch from the sprinklers. 3. Design 
> >criteria for ceiling sprinklers based on 12.1.10 
> >(NFPA 13 2002): 1500sqft/0.20  gpm/sqft  4. 
> >Since we have solid shelving do we need have in 
> >rack sprinklers and need to apply  section 
> >12.3.1.9.2 “Where solid shelving in single-, 
> >double-, and multiple-row racks  exceeds 64 sqft 
> >in are or where the level of storage exceed 6 
> >ft, sprinklers shall be  installed at the 
> >ceiling and below each level of shelving”? It 
> >is not really clear to me that this requirement 
> >applies to miscellaneous storage also. I would 
> >really appreciate you help. Thank you, Anna 
> >Reich 
> >_______________________________________________ 
> >Sprinklerforum mailing list 
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
> >For Technical Assistance, send an email to: 
> >[email protected] To Unsubscribe, 
> >send an email 
> >to:[email protected] (Put 
> >the word unsubscribe in the subject field)
> 
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080  
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to