You're mostly there.  Chap 13 applies equally to storage (no pile  
limit or % of building) when based on storage height.  A warehouse  
with Class I-IV  up to 12 ft follows chap 13.  The issue of in-racks  
is not identified by SprinkCode because chap 13 reverts to chap 11.  
and the occupancy hazard approach (which as a side bar even the QR  
reduction applies for the referenced warehouse).  The solid shelf / in- 
rack requirement is a general requirement for chap 16 but 16.2.1.2 .1  
send you to chap 13 for the criteria and nothing in chap 11 or 13  
requires solid shelf / in-rack protection.  Could this be better  
addressed (ok to say addressed at all), of course.  Keeping in mind  
that this is intended to be addressed as an Occupancy Hazard Approach  
issue, helps to focus the discussion.  Granted on a full warehouse,  
I'd be concerned about the solid shelving but in a low ceiling  
basement especially with the rack along only one wall, I can't say  
that poses the same level of concern and would contend that the  
standard does not require them.

As a note of interest, this was raised as a question to the TC during  
the ROC meeting with limited and mixed opinions (too late in the game  
to actually do anything to the standard).  As I've learned, you can't  
necessarily guess with assurance where a herd of 30 votes will go so  
it will be interesting next cycle to see the answer to the flood of  
proposals on this topic.

Bottom line, you best have this discussion with the AHJ before  
submittals (before a binding bid is even better).

Roland

On Mar 12, 2009, at 7:55 AM, <[email protected]> wrote:

> Would this not meet the definition of Miscellaneous Storage?
>
> 3.9.1.14* Miscellaneous Storage.
> -Storage that does not exceed 12 ft (3.66 m) in height and is  
> incidental to another occupancy use group.
> [you said top shelf was at 5ft.]
> -Such storage shall not constitute more than 10 percent of the  
> building area or 4000 ft2 (372 m2) of the sprinklered area,  
> whichever is greater.
> [is the building at least 20,001 sq. ft. and sprinklered?]
> -Such storage shall not exceed 1000 ft2 (93m2) in one pile or area,  
> and each such pile or area shall be separated from other storage  
> areas by at
> least 25 ft (7.62 m).
> [you stated the shelving area is approx. 680 sq. ft.]
>
>
>
> Linens = Class III or Class IV commodity.
>
> If you meet the criteria for the Misc. Storage definition it would  
> seem reasonable that the room could be protected by ceiling  
> sprinklers alone.  Based on NFPA 13, 2007, Table 13.2.1, for Class  
> IV, storage <10ft. you're looking at OH2  with 250 gpm hose and no  
> in-rack sprinklers and this covers shelf type configuration.
>
> Also in A.8.6.6 it mentions shelves along the wall which are not  
> directly below sprinklers do not have the 18" clearance restriction.
>
>
>
> Craig L. Prahl, CET