No sweat and true. Alarm guys afraid to flow water/sprinkler guys afraid to set off an alarm. If'n you cain't do da otha guy's job right them don't do it a t'all. Since you went this way I recognized that many would focus on the procedure and I was addressing the results. Together we all make an awesome team. We should form a national all-stars company and immediately go broke while we ponde the issues while the trunk slammers do the work. Scary! Abort! Abort! Forget the idea.
On Tue, Mar 24, 2009 at 6:01 PM, John Drucker <[email protected]> wrote: > Ron, > > I felt compelled to point out the code requirements. Unlike your analogy > there are those that actually test waterflow switch and deem it a vane type > waterflow test by merely moving the actuator arm couple with sprinkler > contractors who are afraid of tripping the building fire alarm by blocking > the movement of the actuator arm. Just wanted to make sure no one thought > otherwise. > > Sincerely > > John Drucker > Fire Protection Subcode Official > Red Bank, NJ > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Ron Greenman > Sent: Tuesday, March 24, 2009 6:36 PM > To: [email protected] > Subject: Re: Concurrent Testing > > John, > > I was just throwing out hypotheticals and not intending to be the > prophet. My point was that testing is for a purpose beyond itself and > before deciding that two tests are equivalent you have to determine > what each is looking for. Maybe the same thing, maybe the same thing > in part and maybe totally different things. A case in point would be > "a backflow test" which means exactly opposite things depending on > whether you're the sprinkler guy or the backflow guy. Procedures, as > you've shown, can help define the test and certainly proscribes the > procedure. Perhaps I should have stayed away from 72 and 25 and just > stuck to my light analogy. Are we testing for light (does it occur or > not)? Are we testing to see if the bulb is in good order? Are we > testing to see if electricity gets to the socket? Are we testing the > electrical operation of the switch? Or are we just testing to see if > the lever moves from down to up when pushed? I know every morning when > I operate my light switch whether or not the interior BPA system is up > to speed. Back a few decades ago we accidently tested what would > happen should a cascading overload occur in the Northeast due to the > failure of an overloaded shunt relay. Now that was a test. > > On Tue, Mar 24, 2009 at 2:24 PM, John Drucker <[email protected]> > wrote: >> 2007 NFPA-72 Table 10.4.2.2(i) Test Methods >> Mechanical, electrosonic, or pressure-type waterflow device >> Water shall be flowed through an inspector's test connection indicating > the >> flow of water equal to that from a single sprinkler of the smallest > orifice >> size installed in the system for wet-pipe systems, or an alarm test bypass >> connection for dry-pipe, pre-action, or deluge systems in accordance with >> NFPA 25, Standard for the Inspection, Testing, and Maintenance of >> Water-Based Fire Protection Systems. >> >> 2007 NFPA-25 5.3.3.3 >> Testing the waterflow alarms on wet pipe systems shall be accomplished by >> opening the inspector's test connection. >> >> 2007 NFPA-25 5.3.3.3.1 >> Where freezing weather conditions or other circumstances prohibit use of > the >> inspector's test connection, the bypass connection shall be permitted to > be >> used. >> >> Hope this helps >> >> Sincerely >> >> John Drucker >> Fire Protection Subcode Official >> Red Bank, NJ >> >> >> _______________________________________________ >> Sprinklerforum mailing list >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> For Technical Assistance, send an email to: [email protected] >> >> To Unsubscribe, send an email to:[email protected] >> (Put the word unsubscribe in the subject field) >> > > > > -- > Ron Greenman > at home.... > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)