State fire marshal and local fire departments do not have the manpower to 
inspect all the facilities on a regular basis.  That is why they depend on the 
owner to employ a licensed contractor to do the inspection and then submit the 
reports.   One jurisdiction we dealt with recently stated it would take 3 years 
to inspect the major facilities within their jurisdiction, that doesn't include 
the "less significant" occupancies.  They don't have the funding to hire more 
people and they are very limited on resources.  

Many of the larger commercial or industrial facilities have inspections 
performed by their insurance underwriter or their site safety personnel.  They 
don't leave inspection tags and unless you ask for their report, the owner 
isn't going to share it with you.  He might not share it with you even if you 
do ask.  So just because there's not a tag you can't always assume there have 
been no inspections.  


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rodney Hamm
Sent: Wednesday, March 25, 2009 7:35 PM
To: [email protected]
Subject: Re: Concurrent Testing


..................
 

I will add one additional point...the enforcement of these requirements should 
improve. We have a problem in Georgia anyway, I wonder if the problem is 
nationwide? I have visited way too many facilities in Georgia and throughout 
the Southeastern United States which have expired inspection tags and there 
area a significant percentage of locations which have NEVER even had an 
inspection completed by a certified sprinkler contractor or a certified alarm 
company. The larger commercial facilities (likelihood of a more severe fire 
incident in many instances) located in the smaller towns and/or outside of city 
limits are more likely to have this problem than the smaller facilities. Seems 
like the fire department inspectors do not visit or do not ask about fire 
inspections at the larger facilities; based on my experience, inspections are 
warranted MUCH more at these facilities than most of the smaller locations. I 
am generally against government regulation, but maybe each state shoul
 d consider a copy of the current fire inspection forms to verify inspections 
have been performed by a certified sprinkler contractor and a certified fire 
alarm company prior to issuing the annual business license or possibly some 
other annual renewal. If the company does not provide the required 
verification, send the fire department inspectors out for a quick visit to 
discuss the issue. The fact that it is required to obtain the annual business 
license would probably be enough incentive for most companies.

 

Rodney K. Hamm, P.E.
President/Owner
Falcon Fire Protection
Office  (478) 953-1677

Cell  (478) 396-6988

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)